[EnergyPlus_Support] Re: regeneration coil



There is not any error because I don't insert any regeneration air 
heater under DESICCANT DEHUMIDIFIER section. I would a water coil as 
regeneration coil, not a gas or electric one, and I'm trying a 
different strategy. I "manually" put a water coil just before the 
Desiccant Heat Exchanger, and control it with a CONTROLLER:SIMPLE 
controller and a SCHEDULE:SETPOINT setpoint on air outlet node. Thus, 
I don't get any error, but the coil is always off. Maybe it is not 
possibile to control a coil placed on relief air stream. 
What do you think? 


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad 
<RRaustad@...> wrote:
>
> The desiccant dehumidifier only allows an electric or gas heating 
coil 
> in the regeneration air stream. Without one of these heating coil 
types, 
> you should get an error. Is there any errors in the err file?
> 
> davide.loba wrote:
> >
> > Thank you Richard for your reply.
> > I have already "listed" the coil in the OUTSIDE AIR SYSTEM 
EQUIPMENT,
> > as last component, but I have the same problem. Also the schedules
> > seem to be ok.
> > Have you got another advice?
> > Loba
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > Did you "list" the HW coil type and name in the Outside Air 
System
> > object?
> > > You would also want the HW coil to turn on only when the 
desiccant
> > > system is on. The only way I can think of is to manually create 
an
> > > availability schedule for the HW coil based on the times when 
the
> > > desiccant system operates.
> > >
> > > davide.loba wrote:
> > > >
> > > > Hi all,
> > > >
> > > > I have a problem with a desiccant dehumidifier, placed in the
> > outside
> > > > air system. I need to simulate a hot water coil as 
regeneration
> > air
> > > > heater, instead of a gas coil. To do that, I left blank the 
fields
> > > > about the regeneration air heater in DESICCANT DEHUMIDIFIER
> > object, and
> > > > I put a COIL:Water:SimpleHeating coil in the outside air 
system.
> > To
> > > > control it, I use a CONTROLLER:SIMPLE controller, with the air
> > outlet
> > > > node as control_node, and water inlet node as actuator_node.
> > There is a
> > > > SET POINT:MANAGER:SCHEDULED fixed setpoint temperature (70°C) 
on
> > air
> > > > outlet node.
> > > > The simulation ends correctly, without any severe error, but 
the
> > > > regeneration coil doesn't work: "total water heating coil 
rate" is
> > > > always 0.
> > > > Is it possibile to simulate this type of system?
> > > >
> > > > Thanks in advance for your help.
> > > >
> > > > Loba
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu 
<http://www.fsec.ucf.edu>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> >  
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/