[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: regeneration coil
There is not any error because I don't insert any regeneration air
heater under DESICCANT DEHUMIDIFIER section. I would a water coil as
regeneration coil, not a gas or electric one, and I'm trying a
different strategy. I "manually" put a water coil just before the
Desiccant Heat Exchanger, and control it with a CONTROLLER:SIMPLE
controller and a SCHEDULE:SETPOINT setpoint on air outlet node. Thus,
I don't get any error, but the coil is always off. Maybe it is not
possibile to control a coil placed on relief air stream.
What do you think?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> The desiccant dehumidifier only allows an electric or gas heating
coil
> in the regeneration air stream. Without one of these heating coil
types,
> you should get an error. Is there any errors in the err file?
>
> davide.loba wrote:
> >
> > Thank you Richard for your reply.
> > I have already "listed" the coil in the OUTSIDE AIR SYSTEM
EQUIPMENT,
> > as last component, but I have the same problem. Also the schedules
> > seem to be ok.
> > Have you got another advice?
> > Loba
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > Did you "list" the HW coil type and name in the Outside Air
System
> > object?
> > > You would also want the HW coil to turn on only when the
desiccant
> > > system is on. The only way I can think of is to manually create
an
> > > availability schedule for the HW coil based on the times when
the
> > > desiccant system operates.
> > >
> > > davide.loba wrote:
> > > >
> > > > Hi all,
> > > >
> > > > I have a problem with a desiccant dehumidifier, placed in the
> > outside
> > > > air system. I need to simulate a hot water coil as
regeneration
> > air
> > > > heater, instead of a gas coil. To do that, I left blank the
fields
> > > > about the regeneration air heater in DESICCANT DEHUMIDIFIER
> > object, and
> > > > I put a COIL:Water:SimpleHeating coil in the outside air
system.
> > To
> > > > control it, I use a CONTROLLER:SIMPLE controller, with the air
> > outlet
> > > > node as control_node, and water inlet node as actuator_node.
> > There is a
> > > > SET POINT:MANAGER:SCHEDULED fixed setpoint temperature (70°C)
on
> > air
> > > > outlet node.
> > > > The simulation ends correctly, without any severe error, but
the
> > > > regeneration coil doesn't work: "total water heating coil
rate" is
> > > > always 0.
> > > > Is it possibile to simulate this type of system?
> > > >
> > > > Thanks in advance for your help.
> > > >
> > > > Loba
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
<http://www.fsec.ucf.edu>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/