If you report the mass flow or volume flow rate on the inlet to the hot 
water regen coil, is there flow?

Is the controller for the regen coil in the CONTROLLER LIST for the 
OUTSIDE AIR SYSTEM?

Mike


davide.loba wrote:
> There is not any error because I don't insert any regeneration air 
> heater under DESICCANT DEHUMIDIFIER section. I would a water coil as 
> regeneration coil, not a gas or electric one, and I'm trying a 
> different strategy. I "manually" put a water coil just before the 
> Desiccant Heat Exchanger, and control it with a CONTROLLER:SIMPLE 
> controller and a SCHEDULE:SETPOINT setpoint on air outlet node. Thus, 
> I don't get any error, but the coil is always off. Maybe it is not 
> possibile to control a coil placed on relief air stream. 
> What do you think? 
>
>   



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/