Re: [EnergyPlus_Support] Equipment Power Sizing - Heating and Cooling



André

You can also find the equipment sizing results on the *.eio file. But I
think the result depends on the design day. It does no represent the maximum
load verified on the 8760 h. If you want that maximum value (for the 8760h)
you should report the variable "Boiler heating rate" (or something like
that) and than find the maximum value on that column.

E.Sá

2008/3/3, André Lopes <andr_lopes2000@xxxxxxxxx>:
>
>   Good Morning
>
> In what Report is displayed the equipment sizing Power (Boiler or Chiller)
> in kW or other unit?
>
> I want to know the peak Power (Heating and Cooling) on a year (8760
> hours)?
>
> Regards
>
> A L
>
> __________________________________________________________
> Never miss a thing. Make Yahoo your home page.
> http://www.yahoo.com/r/hs
>  
>


[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/