Re: [EnergyPlus_Support] Extraction ventilators
2 options -
1. If the zone with the exhaust fan is served with a COMPACT HVAC
system, then you must run a simulation using the idf with COMPACT HVAC
objects, then take the expidf output file from that run, rename it to a
new filename.idf, and edit to add a ZONE EXHAUST FAN object and add it
to the ZONE EQUIPMENT LIST for that zone.
2. If the zone with the exhaust fan is *not* served with a COMPACT HVAC
system, the you may add the ZONE EXHAUST FAN object in your base idf
file (the one containing COMPACT HVAC objects for other zones.). In
this case, you will need to create a CONTROLLED ZONE EQUIP CONFIGURATION
object, a ZONE EQUIPMENT LIST, and the ZONE EXHAUST FAN. Note, however,
that an exhaust fan in a zone not served by a central HVAC system will
not automatically cause fresh air to enter the building. You must add
INFILTRATION or MIXING from another zone to balance this.
Mike
Ricardo Miranda wrote:
> Hello,
>
> I´m simulating a building that has many exhaust fans. I´m modeling the HVAC
> system with the COMPACT HVAC. The exaust fans have a different schedule than
> the HVAC system. How can I model the energy consumption of the exaust fans
> without the need of an air loop?
>
>
> Regards,
> Ricardo Miranda
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/