Re: [EnergyPlus_Support] multiple unitary multizone systems?



There is no EnergyPlus limit on the number of Compact HVAC unitary 
systems in a single simulation.  Please check with the DesignBuilder 
support team for clarification.

Mike


Minu Agarwal wrote:
>  
>
> Hi Everyone,
>
>  
>
> Is it possible to model more than one unitary multi-zone system in a
> single building in Energy Plus? The documentation on the unitary systems
> does not specify this restriction but the design builder help on
> "compact" systems mentions that only one unitary multi-zone system can
> be applied to a building. Could someone please clarify?
>
>  
>
> Thanks,
>
> Minu Agarwal
>
> CoSA, Buro Happold Consulting Engineers PC
> 100 Broadway 
> New York, NY 10005
> USA
> Telephone:  +1 212 334 2025
> Fax: +1 212 334 5528
>
>  
>
>
>
> This message has been scanned by MailController - www.MailController.altohiway.com
>
>
> [Non-text portions of this message have been removed]
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>  
> Yahoo! Groups Links
>
>
>
>   




The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/