Re: [EnergyPlus_Support] Displacement ventilation problems
Comparing the two input files, the DV case is sized for a cooling supply
air temperature setpoint of 19C and a chilled water design setpoint of
11.67C. The non-DV case uses 12C and 6.7C. But the setpoint managers
were not changed, so the sizing was for one set of temperatures and the
operation was for another. Changing the supply air temp and chilled
water setpoint managers to match the sizing criteria for the non-DV case
now meets setpoint and uses significantly more energy than the DV case.
**NOT SENT YET **
Mike
eric_zhou1223 wrote:
> Hello all,
>
> I was curious and ran the example file called "DisplacementVen-
> 1zoneOffice.idf", and tried to delete DV with decreasing the supply air
> temerature to normal. The results seem to show that using DV costs more
> energy usage or I maybe miss something obvious. Anyone would take a
> look at the uploaded file named "DisplacementVent_1ZoneOffice Del
> DV.idf"? I compared it with the original file "DisplacementVen-
> 1zoneOffice.idf".
>
> Your help would be much appreciated.
>
>
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>
> Yahoo! Groups Links
>
>
>
>
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/