[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Fan appears to operate continuously
Try changing .5 to 0.0.
What type of fan is being used (fan corresponding the the compact
schedule = SchCpct_FanOpern)
JV Dirkes II wrote:
> Dear EPlus support team,
>
> My .csv output file shows a constant value for the "Fan Electric
> Power" report variable for every hour of the year. It's supposed to
> shut down at night and I expect 0 watts during those periods. Please
> help me figure out why the Watts value remains constant.
>
> The System Availability Manager for the fan is set to "cycle on any",
> and the schedule for that fan is intended to allow the fan to shut
> down at night unless there is a load. (I've shown it below).
> Finally, there is also a compact schedule for temperature setpoints
> which lowers the setpoint by ~3C in winter and raises it the same
> amount in summer.
>
> SCHEDULE:COMPACT,
> SchCpct_FanOpern,
> Any Number,
> Through: 31 Dec,
> For: Weekdays SummerDesignDay,
> Until: 06:00,
> .5,
> Until: 19:00,
> 1,
> Until: 24:00,
> .5,
> For: Saturday,
> Until: 08:00,
> .5,
> Until 13:00,
> 1,
> Until: 24:00,
> .5,
> For: Holidays AllOtherDays,
> Until: 24:00,
> .5;
>
> Ideas? Thanks
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/