RE: [EnergyPlus_Support] Very High airflow / ton of cooling



The DX coil model will always issue the severe warning unless you to use
a CFM/ton that lies in the model's range.  If the OA requirements are
large, the DX system's capacity will have to rise to meet them.  

 

I believe what you need to check into is the Zone Sizing object's
outside air method-probably needs to be "Flow/Zone" with the local code
requirements in m3/s set in the Outside Air Per Zone field.  

 

________________________________

From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of JV Dirkes II
Sent: Monday, March 10, 2008 7:49 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Very High airflow / ton of cooling

 

Dear EPlus Support,

I am modeling a building for a LEED project and must prepare a model
using a packaged rooftop AC system for the "baseline". This building
is a professional (medical) office building which must also comply
with minimum airflow requirements set by the local health code. As a
result, my System has over 1000CFM / ton and I get an error when
running the model.

The error is:
** Severe ** Sizing: COIL:DX:COOLINGBYPASSFACTOREMPIRICAL
"CLGCOIL_AH1": Rated air volume flow rate per watt of rated total
cooling capacity is out of range. See Input-Output Reference Manual
for valid range.

My system is a FURNACE:HeatCool object using a
COIL:DX:CoolingBypassFactorEmpirical cooling coil. I have selected
"design day with limit" in the ZONE SIZING (to force the known minimum
airflow rate) and "design day" in the SYSTEM SIZING.

The COIL:DX:COOLINGBYPASSFACTOREMPIRICAL object started out with
"autosize" selected for both Cooling Capacity and Airflow. I later
tried manually inputting the Cooling Capacity without success.

I will very much appreciate suggestions about how to model this
admittedly unrealistic system!

 



[Non-text portions of this message have been removed]



The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/