[EnergyPlus_Support] Re: Zone exhaust fan example



Thanks!

When used with a PTAC, which node should be the exhaust fan's inlet node and which 
should be its outlet node?  I ask because if the HVAC Diagram is not working, I'm not 
quite sure how to check my work.

-Greg

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> The unbalanced air flow warning is just that, a warning to let you know 
> the supply and return (and I think exhaust) flows do not match. The 
> warning is telling you to add mixing or cross-mixing objects to account 
> for the imbalance. You will still get the warnings though. Report the 
> supply, return, and exhaust node volumetric flow rates, set up mixing 
> objects to account for the imbalance. There is also a known issue with 
> HVAC Diagram with that example file. We are working on the solution.
> 
> boulder1259 wrote:
> >
> > I have a five zone building in which outside air enters through the 
> > core zone, and then it is
> > distributed (via cracks around doors, etc) into the four perimeter 
> > zones. I looked through the
> > archives and found a thread (Air Flow between Zones, answered Jan 26, 
> > 2008) that explained
> > how to do this, but I can't get the suggested solution with a zone 
> > exhaust fan to work. I
> > have two problems:
> >
> > 1) Unbalanced airflow (In zone 873, there is unbalanced exhaust air 
> > flow...)
> > 2) The HVAC diagram does not get drawn (Started HVAC Diagram... 
> > Ancestor to the following
> > box is a splitter: OUTSIDE AIR BALANCING FAN)
> >
> > I looked at 5ZoneEndUses.idf, and it seems to have errors, too 
> > (unbalanced airflow, HVAC
> > Diagram errors). Consequently, I don't have a working example that I 
> > can use to get my
> > simulation running.
> >
> > I'd appreciate any help you can offer.
> >
> > Thanks,
> > Greg
> >
> >  
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>





The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
 
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/