RE: [EnergyPlus_Support] pipe losses



Pipe losses are modeled using a Pipe:Interoir or a Pipe:Exterior object.

The plain "Pipe" object does not model any losses.

So, suggest changing your Pipe:Exterior and Pipe:Interior objects to Pipe 
objects to get zero losses.

Another option might be to set the "Pipe Length" to a very small value (e.g., 
0.001 meters) in your existing Pipe:Interior and Pipe:Exterior objects.


>===== Original Message From Minu Agarwal <Minu.Agarwal@xxxxxxxxxxxxxxx> =====
>Hi Everyone,
>
>
>I am trying to set the loss from the pipes to 0.00%. Do you think it
>would be a good idea to set the ambient temperature for the pipe to the
>fluid temperature to eliminate losses? Does anyone know of a better way
>of eliminating piping losses from the equation?
>
>It would be great if someone from the EnergyPlus team could respond.
>
>
>
>Many Thanks
>
>Minu Agarwal
>
>CoSA, Buro Happold Consulting Engineers PC
>100 Broadway
>New York, NY 10005
>USA
>Telephone:  +1 212 334 2025
>Fax: +1 212 334 5528


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/