Re: [EnergyPlus_Support] How to precondition outside air?
There are examples of how to connect a heating coil in an outside air
stream. Search the example files for the "outside air system." This
objects equipment list defines the equipment located in the outside air
steam. One example for a cooling and heating coil connection in an
outside air system is found in 5ZoneAirCooled.idf. I am not sure if
there is an example of an evaporative cooler in an outside air system,
however, the following types of evaporative coolers are allowed in the
outside air stream.
EVAPCOOLER:DIRECT:CELDEKPAD
EVAPCOOLER:INDIRECT:CELDEKPAD
EVAPCOOLER:INDIRECT:WETCOIL
EVAPCOOLER:INDIRECT:RDDSPECIAL
boulder1259 wrote:
>
> I'm trying to model an HVAC system that uses preconditioned outside air.
>
> The system in question uses an evaporative cooler to cool the outside
> air before it reaches
> the main cooling coil (it also has a gas furnace to warm the outside
> as required). I'm looking
> for suggestions as to the proper way to implement outside air
> preconditioning within
> EnergyPlus.
>
> I appreciate any help you can offer.
>
> Thanks,
> Greg
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
========================================================================
Groups related to EnergyPlus_Support
========================================================================
VisualDOE (27 common members)
http://groups.yahoo.com/group/VisualDOE?v=1&t=ipt&ch=email&pub=groups&slk=aftr0&sec=recg
Software/Specific Programmes: VisualDOE Software User Group
paperport (13 common members)
http://groups.yahoo.com/group/paperport?v=1&t=ipt&ch=email&pub=groups&slk=aftr1&sec=recg
Software/Specific Programmes: PaperPort User Self-Support Forum This is the Unof...
OziUsers-L (11 common members)
http://groups.yahoo.com/group/OziUsers-L?v=1&t=ipt&ch=email&pub=groups&slk=aftr2&sec=recg
Software/Specific Programmes: A group for users of the OziExplorer software, inc...
vendorgsm (8 common members)
http://groups.yahoo.com/group/vendorgsm?v=1&t=ipt&ch=email&pub=groups&slk=aftr3&sec=recg
Software/Specific Programmes: SOFTWARE AND SOLUTIONS ALWAYS TESTED!
TC2000-Stocks (7 common members)
http://groups.yahoo.com/group/TC2000-Stocks?v=1&t=ipt&ch=email&pub=groups&slk=aftr4&sec=recg
Software/Specific Programmes: User's Group dedicated to the discussion and excha...
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/