[EnergyPlus_Support] Re: Ice storage system in EnergyPlus



Thank you,Mike! However, this configuration will do affect the 
efficiency of downstream chiller because of lower inlet water 
temperature, I really wonder what difference will this configuration 
make when compared to a real chiller upstream and ice tank priority 
configuration? Moreover, when I tried to check inlet and outlet 
temperatures of both chillers and ice tanks, even the loop outlet 
temperature has achieved -5C and the tank has been fully charged, 
there is still some energy consumption of chillers, is it confusing?
My pump's ration of pump in flow is 0, so I don't think additional 
heat will add to this loop.Or is there any possible reason for this 
instance? Thank you again and I am looking forward to your answer!




--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" 
<mjwitte@...> wrote:
>
> The ice storage units currently only work with component set point 
based 
> control, they do not work with load based controls. 
> 
> The only way to model ice tank priority would be to create a 
second 
> instance of the chiller which is downstream of the ice tank.  Then 
use 
> the setpoint manager schedules to operate only one of the two 
chillers.
> 
> Mike
> 
> 
> mingming_zuo wrote:
> > Hi all, I tried to model ice storage system with different kinds 
of 
> > operation strategy in energyplus such as ice tank 
priority,chiller 
> > priority.By doing these work, i come to a question:what control 
> > strategy of plants in a loop can energyplus achieve? Can it just 
act as 
> > it is said in the input&output reference? I think it may not be 
the 
> > fact. I would like to share some of my failure with you, which 
may help 
> > us have a good understanding of energyplus and make better use 
of it.In 
> > one of my several models, the chiller and ice tank is configured 
in 
> > series with the chiller upstream.Two operation schemes,one is 
Cooling 
> > Load Range Based Operation and the other is Component Setpoint 
Based 
> > Operation, are also defined in the Plant-condenser 
control.Cooling Load 
> > Range Based Operation is set to run during peak hours while 
Component 
> > Setpoint Based Operation runs during the night time. Moreover, 
we 
> > define ,in plant equipment list,the ice tank first and then the 
main 
> > chiller, hoping the ice tank will satisfy the cooling load 
> > first.However the results of this model is really disapointed 
and the 
> > chiller still has its priority in satisfying the cooling load. I 
also 
> > upload an idf file named IceStorage-Series-ChillerUpstream.idf 
which is 
> > an example file with some related parts redefined.I hope it can 
help us 
> > to learn more.
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the 
appropriate folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
under the Documentation link and press the "search" button.
> >  
> > Yahoo! Groups Links
> >
> >
> >
> >
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/