[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [EnergyPlus_Support] Splitting an earth tube
John wrote;
NO. Depending on how strict you are. If you take the dirt near the
building as being warmer than the surrounding area then you have a
counter flow heat exchanger.... and that's not linear with flow
direction length.
I would take two full length tubes with half the surface area per
running foot of the big tube for the thermal calculation, but that's
going to make the blower fan energy wrong......too high; but the blower
energy should be a small fraction of the total earth tube recovery so
it's still a better result.
bye.
Danny Bishop wrote:
>
> hi All
> I have a building that has a single earth tube with two outlets
> feeding two
> separate thermal zones. In order to implement it in E+ I need to split the
> single tube into two equivalent earth tubes - one for each zone. Now
> splitting the flows is easy - I just put the flow coming out of each
> outlet
> to each of the two separated earth tubes.
>
> The question I have is how to adjust the dimensions (Length and
> diameter) of
> the single tube to the two equivalent earth tubes. Is it equivalent
> just to
> use half the length of the original tube for each of the separated tubes?
> cheers
> Danny
>
> [Non-text portions of this message have been removed]
>
>
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/