The only complication in your proposed control strategy seems to be your
desire for the shading to be forced ON from 0 to 8h. Did you try just
controlling with "OnIfHighOutsideAirTemp" for all hours?
Rob Hitchcock
========
Nuno Costa Brandão wrote:
> Hi All,
>
> Just poping this back, hoping that someone gives me some guidance help
>
> Thanks
> Nuno
> ---------------------------------------
> Dear All,
>
> I´m simulating a building with shading(exterior blinds) in its windows.
> The shading control should be as follows:
>
> from 0 to 8h: shading is always on
> from 8h to 21h: shading is on if outside air temperature exceeds 20ºC
> and its off if outside air temperature is less than 20 ºC
> from 21hto 24h: shading is always off
>
> The best approach I could obtain was to define a schedule control
> always equal to 1(meaning that the shading is always on for the 24h)
> and a control setpoint of 20ºC, with the "OnIfHighOutsideAirTemp"
> control, which would override the schedule everytime the out side air
> temp is less then 20ºC. This resulted in a higher costs because
> supplemental heating is needed for the times where the shading is
> always on.
>
> Is there any other alternative to precisely simulate the control
> previously described above?
>
> Thanks for the help
> Nuno
>
>
> Messages in this topic
> <http://groups.yahoo.com/group/EnergyPlus_Support/message/10637;_ylc=X3oDMTM2ZXQ4cnBhBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzEwNjM3BHNlYwNmdHIEc2xrA3Z0cGMEc3RpbWUDMTIwNjM3MTkxMQR0cGNJZAMxMDYzNw-->
> (1) Reply (via web post)
> <http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJxbzM0dm45BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzEwNjM3BHNlYwNmdHIEc2xrA3JwbHkEc3RpbWUDMTIwNjM3MTkxMQ--?act=reply&messageNum=10637>
> | Start a new topic
> <http://groups.yahoo.com/group/EnergyPlus_Support/post;_ylc=X3oDMTJlbzN2NTg5BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTIwNjM3MTkxMQ-->
>
> Messages
> <http://groups.yahoo.com/group/EnergyPlus_Support/messages;_ylc=X3oDMTJlbTdjamsyBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA21zZ3MEc3RpbWUDMTIwNjM3MTkxMA-->
> | Files
> <http://groups.yahoo.com/group/EnergyPlus_Support/files;_ylc=X3oDMTJmNmN2a2R2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2ZpbGVzBHN0aW1lAzEyMDYzNzE5MTA->
> | Photos
> <http://groups.yahoo.com/group/EnergyPlus_Support/photos;_ylc=X3oDMTJlamVpOGRrBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3Bob3QEc3RpbWUDMTIwNjM3MTkxMA-->
> | Members
> <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJlN2dzcmt1BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA21icnMEc3RpbWUDMTIwNjM3MTkxMA-->
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the
> appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
> the Documentation link and press the "search" button.
> Yahoo! Groups
> <http://groups.yahoo.com/;_ylc=X3oDMTJkcDlkanM3BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMjA2MzcxOTEx>
>
> Change settings via the Web
> <http://groups.yahoo.com/group/EnergyPlus_Support/join;_ylc=X3oDMTJma2FvbmRoBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA3N0bmdzBHN0aW1lAzEyMDYzNzE5MTE->
> (Yahoo! ID required)
> Change settings via email: Switch delivery to Daily Digest
> <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx?subject=Email%20Delivery:%20Digest>
> | Switch format to Traditional
> <mailto:EnergyPlus_Support-traditional@xxxxxxxxxxxxxxx?subject=Change%20Delivery%20Format:%20Traditional>
>
> Visit Your Group
> <http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJkMzRvNnNlBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2hwZgRzdGltZQMxMjA2MzcxOTEx>
> | Yahoo! Groups Terms of Use <http://docs.yahoo.com/info/terms/> |
> Unsubscribe
> <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=>
> Recent Activity
>
> *
> 13
> New Members
> <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmdjg3Y2ZhBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEyMDYzNzE5MTA->
> *
> 2
> New Files
> <http://groups.yahoo.com/group/EnergyPlus_Support/files;_ylc=X3oDMTJna2gycG92BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZmaWxlcwRzdGltZQMxMjA2MzcxOTEw>
>
> Visit Your Group
> <http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlYXByaHJxBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTIwNjM3MTkxMA-->
>
> Yahoo! Finance
>
> It's Now Personal
> <http://us.ard.yahoo.com/SIG=13opa0rbd/M=493064.12016257.12445664.8674578/D=groups/S=1705007389:NC/Y=YAHOO/EXP=1206379114/L=/B=ip1rDkLaX9U-/J=1206371914127432/A=4507179/R=0/SIG=12de4rskk/*http://us.rd.yahoo.com/evt=50284/*http://finance.yahoo.com/personal-finance>
>
> Guides, news,
>
> advice & more.
>
> Ads on Yahoo!
>
> Learn more now.
> <http://us.ard.yahoo.com/SIG=13or5kmat/M=493064.12016308.12445700.8674578/D=groups/S=1705007389:NC/Y=YAHOO/EXP=1206379114/L=/B=i51rDkLaX9U-/J=1206371914127432/A=3848643/R=0/SIG=131q47hek/*http://searchmarketing.yahoo.com/arp/srchv2.php?o=US2005&cmp=Yahoo&ctv=Groups4&s=Y&s2=&s3=&b=50>
>
> Reach customers
>
> searching for you.
>
> Yahoo! Groups
>
> Find balance
> <http://us.ard.yahoo.com/SIG=13o2378t9/M=493064.12016238.12823558.8674578/D=groups/S=1705007389:NC/Y=YAHOO/EXP=1206379114/L=/B=jJ1rDkLaX9U-/J=1206371914127432/A=5286666/R=0/SIG=11in3uvr5/*http://new.groups.yahoo.com/planforabalancedlife>
>
> between nutrition,
>
> activity & well-being.
>
> .
>
> __,_._,__
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/