Re: [EnergyPlus_Support] Shading Control issue
You could use the Schedule:File:Comma object to define the blind
schedule. Open the weather file in a spreadsheet. Insert a new column
for hour of day and initialize to 1 to 24 for all days. Use the IF
command to calculate the hourly schedule value. IF (hour < 9, 1, IF(hour
> 20, 0, IF(OAT < 20, 0,1))). Do this for 8760 hours. Save this
schedule as comma delimited to create the Schedule:File:Comma object.
What this hourly schedule can not do is interpolate the weather data to
turn the blinds on/off at intervals less than 60 minutes.
Nuno Costa Brandão wrote:
>
> Hi All,
>
> Just poping this back, hoping that someone gives me some guidance help
>
> Thanks
> Nuno
> ---------------------------------------
> Dear All,
>
> I´m simulating a building with shading(exterior blinds) in its windows.
> The shading control should be as follows:
>
> from 0 to 8h: shading is always on
> from 8h to 21h: shading is on if outside air temperature exceeds 20ºC
> and its off if outside air temperature is less than 20 ºC
> from 21hto 24h: shading is always off
>
> The best approach I could obtain was to define a schedule control
> always equal to 1(meaning that the shading is always on for the 24h)
> and a control setpoint of 20ºC, with the "OnIfHighOutsideAirTemp"
> control, which would override the schedule everytime the out side air
> temp is less then 20ºC. This resulted in a higher costs because
> supplemental heating is needed for the times where the shading is
> always on.
>
> Is there any other alternative to precisely simulate the control
> previously described above?
>
> Thanks for the help
> Nuno
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/