Re: [EnergyPlus_Support] Re: Constant Air Volume with Heat Recovery?



You can't replace the coils in the unitary systems with water coils. But 
in SmOff the
systems are modeled as individual components on an air loop. You would 
replace
the DXSystem:AirLoop with a chilled water coil and the COIL:Gas:Heating with
a hot water coil. An you would need to add a Controller:Simple to 
control each water
coil.

Fred Buhl

anarui.oliveira wrote:
> Thanks.
> I've been looking at those unitary systems, but do they really allow 
> me to replace the coils? They show up as necessary inputs and as 
> those specific types of coils in the definition of unitary equipments?
> Ana.
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Fred Buhl <wfbuhl@...> 
> wrote:
>   
>> It sounds sort of like a single zone system - there's examples of 
>> packaged single zone systems
>> (for instance SmOffPSZ). You'd have to repalce the DX and Gas coils 
>>     
> with 
>   
>> chilled and hot water
>> coils. And add heat recovery.
>>
>> Fred Buhl
>>
>> anarui.oliveira wrote:
>>     
>>> Hello, everyone.
>>>
>>> I can't seem to find a model in E+ that corresponds to:
>>> - a dedicated AHU (with heat recovery) serving only one zone,
>>> - with constant volumetric air flow (always 100% outside air)
>>> - using a chilled water loop and a hot water loop for air 
>>>       
> conditioning
>   
>>> - where the zone temperature control is done directly and 
>>>       
> uniquely by 
>   
>>> turning the coils on/off at the System level (AHU), rather then 
>>> changing the air flow or doing reheat/recool at zone level.
>>>
>>> Can I include Heat Recovery in any HVAC objects, other than the 
>>>       
> system 
>   
>>> level AHUs, to solve this issue with a zone level equipment or 
>>>       
> other 
>   
>>> simplification?
>>>
>>> All ideas are welcome.
>>> Regards,
>>> Ana Rui.
>>>
>>>
>>> ------------------------------------
>>>
>>> The primary EnergyPlus web site is found at:
>>> http://www.energyplus.gov
>>>
>>> The group web site is:
>>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>>
>>> Attachments are not allowed -- please post any files to the 
>>>       
> appropriate folder in the Files area of the Support Web Site.
>   
>>> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
>>>       
> under the Documentation link and press the "search" button.
>   
>>> Yahoo! Groups Links
>>>
>>>
>>>
>>>
>>>       
>
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>   


[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/