The error message made that much pretty clear.  Apparently "autosize"
is not particularly smart and does not allow the minimum value to
actually BE the minimum value?  It seems that a warning is called for,
but not a fatal error.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> You get the error because the autosized maximum air flow rate is
smaller 
> than the minimum air flow rate. Look at the eio file to determine what 
> the autosized value is for the outside air maximum flow rate. Then 
> compare that number to your fixed value for minimum outside air flow 
> rate. Use either value for both the maximum and minimum outside air
flow 
> rates.
> 
> JV Dirkes II wrote:
> >
> > Dear EPlus Forum,
> >
> > When I set the CONTROLLER:OUTSIDE AIR "minimum outside air flow rate"
> > input to a fixed value and the "maximum outside air flow rate" to
> > "autosize", I receive an error.
> >
> > ** Severe ** For CONTROLLER:OUTSIDE AIR: OACONTROLLER_AH1
> > ** ~~~ ** maximum outside air flow rate (2.83) < minimum
> > outside air flow rate (2.83)
> >
> > In my mind, it seems appropriate to establish a minimum airflow, which
> > in this case is for exhaust fans, and then let the program establish
> > the maximum (which should be the larger of either the specified
> > minimum or economizer operation). Why does this error occur?
> >
> > p.s., It goes away when I "autosize" the minimum value.
> >
> >  
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/