[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: [EnergyPlus_Support] Heating coil sensible part-load ratio
Thank you!
The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653
_____
From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Griffith, Brent
Sent: Friday, March 28, 2008 11:05 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: RE: [EnergyPlus_Support] Heating coil sensible part-load ratio
Look at it the wording this way, it isn't "Sensible Part" Load
Ratio--its Sensible "Part Load Ratio". The part load isn't referring to
sensible versus latent, its referring to what part of this time step the
coil is on. It's a fraction of full load sensible heating. Remember
the simulation often has a time step that is longer than cycling period,
this leads to part load ratios for all sorts of things...
Not sure why you would be getting the error (or rather I don't imagine
its very helpful to note it is because the numerical solver
SolveRegulaFalsi returned a SolFlag = -1). But the convergence is
pretty close (0.14%), so it sounds safe to ignore.
________________________________
From: EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
[mailto:EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com] On Behalf Of JV Dirkes II
Sent: Friday, March 28, 2008 6:27 PM
To: EnergyPlus_Support@ <mailto:EnergyPlus_Support%40yahoogroups.com>
yahoogroups.com
Subject: [EnergyPlus_Support] Heating coil sensible part-load ratio
Dear EPlus Forum,
I'd like some help understanding the error below. I don't know what a
"sensible part load ratio" refers to for a COIL:GAS:HEATING object
within a Furnace:HeatCool object. It sounds like the sensible heat
ratio for a DX cooling coil, but that makes no sense for heating....
** Warning ** Heating coil control failed to converge for
Furnace:HeatCool:AH_03
** ~~~ ** Iteration limit exceeded in calculating heating
coil sensible part-load ratio.
** ~~~ ** Sensible load to be met by heating coil = 107013.56
(watts), sensible output of heating coil = 107158.23 (watts), and the
simulation continues.
Thanks!
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/