Dear Brent,

Thank you for the reply, I think your information is quite useful. It is really strange that a component like this exists in EnergyPlus and there is no available example or simulation made by someone. The problem we are facing now is with the normalization object for the CHP. We must define an object, a performance curve for the electrical and the thermal efficiency of the CHP. These objects have to be TriQuadratic curves with 12 coefficients. I would like to ask you if you know how we can find information for these coefficients,  would it be more preferable to wait for the CHP example? Thank you again for the reply.

Best regards

Tasos Ioannou

"Griffith, Brent" <brent_griffith@xxxxxxxx> wrote:                             Tasos, 
 
 The next release of EnergyPlus (version 2.2 due out in April 2008)
 should include an example file for micro cogeneration.  The current
 version 2.1 has some problems that make it difficult to make good use of
 the Generator:Micro CHP component model.  The micro CHP model has the
 heat exchanger already inside it.  
 
 The plant topology I find useful for cogeneration uses a water heater as
 a storage tank.  There are two Plant loops (and no condenser loop).  The
 water heater's Source side is connected to the cogenerator and the Use
 side is connected to zone heating coils and service hot water uses. 
 
 ________________________________
 
 From: EnergyPlus_Support@xxxxxxxxxxxxxxx
 [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of tasos.ioannou
 Sent: Monday, March 31, 2008 3:11 AM
 To: EnergyPlus_Support@xxxxxxxxxxxxxxx
 Subject: [EnergyPlus_Support] CHP simulation example?
 
 Dear Forum,
 
 Our team is trying to model a micro CHP unit for a carbon zero
 building. We have a lot of questions about how to connect the heating
 part of the CHP with the rest of the heating system of the building.
 We are thinking of making a condenser loop that will contain a heat
 exchanger which will be representing the heat recovery unit of the
 CHP. The water that will be condensed through this process and still
 will be warm will be then sent to the Plant loop in the hot water
 branch and from there to the zones. But what can this branch be? A
 pipe maybe? These are just thoughts of course.
 
 I would like to ask you if there is any CHP example (that is correct
 and able to be simulated)that you could upload? This would be of
 enormous help.
 
 Best Regards
 
 Tasos Ioannou
 
 [Non-text portions of this message have been removed]
 
 
     
                                       

       
---------------------------------
You rock. That's why Blockbuster's offering you one month of Blockbuster Total Access, No Cost.

[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/