Neslihan:
Yes, you can use revised discharge coefficient to include impact of shading
devices. Since the airflow rate is assumed to be proportional to the opening
area and discharge coefficient, the open area change can obtain the same
impact.
It should be pointed out that linear interpolation is used to calculate the
open area and discharge coefficient based on the opening factor. If the
shading devices have highly non-linear impact on airflows, this method may
not work well.
Best regards,
Lixing Gu
----- Original Message -----
From: "neslihan turkmenoglu" <neslihanturkmenoglu@xxxxxxxxx>
To: <energyplus_support@xxxxxxxxxxxxxxx>
Sent: Tuesday, April 01, 2008 11:02 AM
Subject: [EnergyPlus_Support] detailed opening-discharge and
>
> Hi
> I want to check the way I used for flow rate
> calculation.
> Energyplus doesn't consider the effects of shading
> devices on volume flow rates. I calculated discharge
> coefficients for every alternatives of openings with
> shading device but I used the same opening width and
> height factors or every alternatives in energyplus as
> I used opening areas in the calculation.Is it the
> right way?
> If I didn't do it like this I don't have any idea how
> to define start point for an opening occuring on
> window with for example with a blind hving a lot of
> start points.
>
> Thank you vey much for your help
>
>
>
>
> ____________________________________________________________________________________
> You rock. That's why Blockbuster's offering you one month of Blockbuster
> Total Access, No Cost.
> http://tc.deals.yahoo.com/tc/blockbuster/text5.com
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate
> folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/