[EnergyPlus_Support] Re: Fwd: Outside air mixer is recirculating return flow: Why?



Thank you for the insight.
I'll study the plenum approach option... see if it may be applied 
here.
I don't suppose there is some other way to exchange air between 
zones in a way that the HVAC components will aknowledge it correctly?

Ana.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Fred Buhl <wfbuhl@...> 
wrote:
>
> Ana,
> 
> anarui.oliveira wrote:
> > Thank you, but I checked the zones receiveing the exhaust fans 
flow: 
> > the corresponding inlets are registering that incoming flow, and 
the 
> > return flow from those zones is summing that airflow to the 
airflow 
> > directly insufflated to that zone. The return flow after the air 
> > mixer (after collecting all zones return flows) is correct.
> > Everything checks out until the return flow reaches the Air 
Mixing 
> > Box; if E+ can recognize and properly account the passage of 
airflow 
> > introduced by the fan, why would it create a problem further 
ahead?
> >   
> The system air balance is done at the outside air mixer, since 
this is 
> where the decision has
> to be made on how much outside air to bring in. The system code 
keeps 
> track of the total
> air exhausted, but assumes that it all is really exhauste, not 
going to 
> another zone.
> > I did what you suggest in previous versions of my model...
> > I'm insisting to get it working this way for two reasons:
> >
> > 1- My buildings' HVAC project actually works like that; it 
collects 
> > all its return flow in uncontrolled zones, rather than in the 
zones 
> > that are being controlled and where the flow is being 
insufflated, 
> > and since I have a heat recovery unit, I thought it might 
> > influenciate the results; I don't really have enough experience 
to 
> > say if it makes that much difference, but...
> >   
> Could you make these uncontrolled return zones into plenum zones? 
> Plenums don't have to be
> actual plenums - they are just uncontrolled zones with return air 
> passing through.
> 
> Fred Buhl
> > 2- The other reason is the 2:1 limit on the insufflated vs. 
return 
> > flow in the heat exchanger, since this and other projects 
actually 
> > have a higher ratio, so, in order not to overestimate the heat 
> > recovery potential, I would want to send the extra airflow to a 
dummy 
> > zone with (nearly) exterior conditions.
> >
> > Thanks again,
> > Ana.
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Fred Buhl <wfbuhl@> 
> > wrote:
> >   
> >> I suspect it is due to the exhaust fans. Have you tried using 
Cross 
> >> Mixing objects instead?
> >> EPlus will assume the exhaust fans exhaust the air - and will 
not 
> >>     
> > send 
> >   
> >> it to another zone.
> >>
> >> Fred Buhl
> >>
> >> anarui.oliveira wrote:
> >>     
> >>> ... Apparently, it is recirculating the exact amount of 
airflow 
> >>>       
> > that 
> >   
> >>> I am trying to pass from some zones to adjacent zones with 
> >>>       
> > exhaust 
> >   
> >>> fans (the aim was precisely to force the return path to 
collect 
> >>>       
> > its 
> >   
> >>> air flow from those areas, which are not controlled). Is it 
> >>>       
> > related? 
> >   
> >>> I can't do that?
> >>>
> >>>
> >>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "anarui.oliveira" 
> >>> <anarui.oliveira@> wrote:
> >>>
> >>> Hello.
> >>>
> >>> I have set up a VAV system, with heat recovery, and manually 
> >>>       
> > entered 
> >   
> >>> the exact same value for for all outside airflow variables and 
> >>> airflow variables (the "air primary loop", 
> >>>       
> > the "controller:outside 
> >   
> >>> air", the fan, the heat exchanger,... all have the same 
airflow 
> >>> defined).
> >>> I hoped, with this, to establish that the supply air should be 
> >>>       
> > 100% 
> >   
> >>> OA, and no return air should be recirculated, but rather 
become 
> >>>       
> > all 
> >   
> >>> reflief air, passing through the heat excahnger, as I had 
> >>>       
> > understood 
> >   
> >>> from previous analysis...
> >>>
> >>> Msg 9808:
> >>>
> >>> Yes. this will provide 100% outside air with heat recovery and 
no
> >>> recirculation. However, the outside air flow will never be 
more 
> >>>       
> > than 
> >   
> >>> the system supply flow rate. So, when the VAV terminal units 
> >>>       
> > reduce 
> >   
> >>> the total system flow rate, the outside air flow rate will be 
> >>> reduced to match.
> >>> Mike
> >>>
> >>> On 12 Jan 2008 at 1:44, anarui.oliveira wrote:
> >>>   
> >>>       
> >>>> Hello again.
> >>>> If in the Compact HVAC:System:VAV I set:
> >>>> - Heat recovery to sensible
> >>>> - both the Fan Max and Min Flow rate, and both the Max and 
Min 
> >>>>     
> >>>>         
> >>> Outside Air Flow rate to the same value,
> >>>   
> >>>       
> >>>> - and Outside Air Control Type to fixed minimum
> >>>> do I get a system that exhausts to the outside all the return 
> >>>>         
> > air 
> >   
> >>>>     
> >>>>         
> >>> of the ATU, recirculating none to the inside and substituting 
it 
> >>>       
> > by 
> >   
> >>> outside air, at a fixed rate, but first using the return air 
to 
> >>>       
> > do 
> >   
> >>> sensible heat recovery?
> >>>
> >>> BUT, reporting the flow at the different nodes, I find that, 
> >>> although the zone return airflows add up correctly to the "air 
> >>>       
> > loop 
> >   
> >>> inlet" flow, the Outside Air Mixing Box is diverting about 37% 
of 
> >>> that return flow and adding it to the outside air flow 
supplied 
> >>>       
> > by 
> >   
> >>> the heat exchanger... which was causing the 2:1 limit error I 
was 
> >>> getting at the heat exchanger, altough the defined exhaust 
fans 
> >>>       
> > are 
> >   
> >>> not taking out nearly that much flow (in fact, I checked that 
the 
> >>> return flow is as expected, until it reaches the Air Mixer)...
> >>> The zone air distribution equipment is Direct Air in all zones 
> >>> served by this Air Loop, so there's no change in the airflow 
> >>>       
> > there...
> >   
> >>> And I can't figure out what is controlling this behaviour or 
how 
> >>>       
> > to 
> >   
> >>> change it to the desired model...
> >>>
> >>> Can anyone help me? I'd really like to get this one working.
> >>>
> >>> Best regards,
> >>> Ana Rui.
> >>>
> >>> --- End forwarded message ---
> >>>
> >>>
> >>>
> >>> ------------------------------------
> >>>
> >>> The primary EnergyPlus web site is found at:
> >>> http://www.energyplus.gov
> >>>
> >>> The group web site is:
> >>> http://groups.yahoo.com/group/EnergyPlus_Support/
> >>>
> >>> Attachments are not allowed -- please post any files to the 
> >>>       
> > appropriate folder in the Files area of the Support Web Site.
> >   
> >>> EnergyPlus Documentation is searchable.  Open 
EPlusMainMenu.pdf 
> >>>       
> > under the Documentation link and press the "search" button.
> >   
> >>> Yahoo! Groups Links
> >>>
> >>>
> >>>
> >>>   
> >>>       
> >> [Non-text portions of this message have been removed]
> >>
> >>     
> >
> >
> >
> > ------------------------------------
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the 
appropriate folder in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf 
under the Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> >   
> 
> 
> [Non-text portions of this message have been removed]
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/