[EnergyPlus_Support] Re: Air handler Heating coil operates in the summer



Dear Don,

Two different SET POINT MANAGER:SCHEDULED objects refer to the same
compact schedule set for 12.8C at all times.  Both SET POINT
MANAGER:SCHEDULEDs use "NodeOut_Air_AH1" as the set point node.

It is a draw through configuration, so you're correct re: making
account for the fan heat, however here is a typical result for one
time interval (in order as the air moves through the air handler):

Mixed air Temp:   66.3F
CC leaving temp:  49.8F
HC leaving temp:  50.8F (HC warms the air 1F)
Fan leaving temp: 55.0F (Fan warms the air 4.2F)



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Don Shirey <shirey@...> wrote:
>
> Sounds like the cooling coil is operating to overcome the cooling load 
> and the supply air fan heat.
> 
> Where are you setting your setpoint temperatures?  At the outlet of the 
> cooling and heating nodes?  What type of setpoint managers are you
using?
> 
> JV Dirkes II wrote:
> > Dear EPlus Forum,
> >
> > My model has an air loop with a single branch as shown below.  The
> > heating and cooling coils are both set to:
> > a) use a constant 55F / 12.8C discharge temperature,
> > b) measured at the identical node (the outlet node for the AHU).
> >
> > During the summer design day operating hours, the temperature leaving
> > the cooling coil is a few tenths of a degree C below what is needed,
> > so the heating coil operates to boost the temp.  This, of course,
> > causes additional energy use.  What causes it and how can I
elimimate it?
> >
> > Thanks in advance!
> >
> > BRANCH,
> > Branch_AirLoop_AH1,
> > 11.3268,
> > OUTSIDE AIR SYSTEM,
> > OASystem_AH1,
> > NodeIn_RA_AH1,
> > NodeOut_MA_AH1,
> > PASSIVE,
> > COIL:WATER:COOLING,
> > ClgCoil_AH1,
> > NodeOut_MA_AH1,
> > NodeOut_ClgCoilAir_AH1,
> > PASSIVE,
> > COIL:GAS:HEATING,
> > HtgCoil_AH1,
> > NodeOut_ClgCoilAir_AH1,
> > NodeOut_HtgCoilAir_AH1,
> > PASSIVE,
> > FAN:SIMPLE:CONSTVOLUME,
> > SFan_AH1,
> > NodeOut_HtgCoilAir_AH1,
> > NodeOut_Air_AH1,
> > ACTIVE;
> >
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/