Re: [EnergyPlus_Support] Minimum Inlet Air Temperature for Heat Pump



The limit of 5C is about as low as you can go before ice builds up on 
the evaporator. There are no defrost calculations in the HP water 
heater, so you can't go below that limit. For cold climates, you can 
blend space air with outside air to keep the temperature above 5C. A 
schedule is used to accomplish this (last input in object), so you can 
blend air only when needed. You will also need to set up the nodes 
correctly for this to work.

anarui.oliveira wrote:
>
> Hi.
>
> Can anyone tell me why, in the "Heat Pump:Water Heater" model,
> the "Minimum Inlet Air Temperature for Heat Pump Compressor Operation"
> is 5ºC? Couldn't find any mention to it the documentation.
>
> How can I model a HeatPump that is used for heating water for a
> climatization system (with Hot Water coils), using outside air, in
> regions where the outdoor temperature drops below 5ºC?
>
> Regards,
> Ana Rui.
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/