Re: [EnergyPlus_Support] sizing factor
My apologies for the slow response.
EnergyPlus does not currently have separate sizing factors for heating and
cooling. The EnergyPlus sizing factor is applied to the supply air volume flow
rate determined for a given zone. This adjusted flow rate is then used to
compute coil sizes for heating and cooling coils based on the user-specified
supply air temperatures in the SYSTEM SIZING object.
By specifying different supply air temperatures in the zone sizing object and
the system sizing object, you can force individual coils to be sized larger or
smaller. But this is a trial and error approach unless you know the design
mixed air temperature and can compute the required supply air temperature to
get the desired sizing factor.
Mike
On 19 Mar 2008 at 14:52, Minu Agarwal wrote:
> Dear All,
>
>
>
> Is it possible to specify different sizing factors for heating and
> cooling design? Could somebody tell me how it could be done? The I/O
> file mentions that sizing factor can be specified at the building level
> or the zone level but the same factor is applied to heating and cooling
> sizing run.
>
>
>
>
>
> Thank You,
>
> Minu
>
> CoSA, Buro Happold Consulting Engineers PC
> 100 Broadway
> New York, NY 10005
> USA
> Telephone: +1 212 334 2025
> Fax: +1 212 334 5528
>
>
>
>
>
> This message has been scanned by MailController - www.MailController.altohiway.com
>
>
> [Non-text portions of this message have been removed]
>
>
> ========================================================================
> Groups related to EnergyPlus_Support
> ========================================================================
>
> VisualDOE (27 common members)
> http://groups.yahoo.com/group/VisualDOE?v=1&t=ipt&ch=email&pub=groups&slk=aftr0&sec=recg
> Software/Specific Programmes: VisualDOE Software User Group
>
> paperport (13 common members)
> http://groups.yahoo.com/group/paperport?v=1&t=ipt&ch=email&pub=groups&slk=aftr1&sec=recg
> Software/Specific Programmes: PaperPort User Self-Support Forum This is the Unof...
>
> OziUsers-L (11 common members)
> http://groups.yahoo.com/group/OziUsers-L?v=1&t=ipt&ch=email&pub=groups&slk=aftr2&sec=recg
> Software/Specific Programmes: A group for users of the OziExplorer software, inc...
>
> vendorgsm (8 common members)
> http://groups.yahoo.com/group/vendorgsm?v=1&t=ipt&ch=email&pub=groups&slk=aftr3&sec=recg
> Software/Specific Programmes: SOFTWARE AND SOLUTIONS ALWAYS TESTED!
>
> TC2000-Stocks (7 common members)
> http://groups.yahoo.com/group/TC2000-Stocks?v=1&t=ipt&ch=email&pub=groups&slk=aftr4&sec=recg
> Software/Specific Programmes: User's Group dedicated to the discussion and excha...
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/