RE: [EnergyPlus_Support] sizing factor



Hi Mike,

Thanks for the work around. Could you also say what is the
difference/relationship between the zone sizing factor under ZONE SIZING
and the zone air supply factor under COMPACT HVAC:ZONE:VAV?

 

Minu Agarwal

CoSA, Buro Happold Consulting Engineers PC
100 Broadway 
New York, NY 10005
USA
Telephone:  +1 212 334 2025
Fax: +1 212 334 5528

________________________________

From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Michael J.
Witte
Sent: Friday, April 11, 2008 1:46 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] sizing factor

 

My apologies for the slow response.

EnergyPlus does not currently have separate sizing factors for heating
and 
cooling. The EnergyPlus sizing factor is applied to the supply air
volume flow 
rate determined for a given zone. This adjusted flow rate is then used
to 
compute coil sizes for heating and cooling coils based on the
user-specified 
supply air temperatures in the SYSTEM SIZING object.

By specifying different supply air temperatures in the zone sizing
object and 
the system sizing object, you can force individual coils to be sized
larger or 
smaller. But this is a trial and error approach unless you know the
design 
mixed air temperature and can compute the required supply air
temperature to 
get the desired sizing factor.

Mike

On 19 Mar 2008 at 14:52, Minu Agarwal wrote:

> Dear All,
> 
> 
> 
> Is it possible to specify different sizing factors for heating and
> cooling design? Could somebody tell me how it could be done? The I/O
> file mentions that sizing factor can be specified at the building
level
> or the zone level but the same factor is applied to heating and
cooling
> sizing run.
> 
> 
> 
> 
> 
> Thank You,
> 
> Minu
> 
> CoSA, Buro Happold Consulting Engineers PC
> 100 Broadway 
> New York, NY 10005
> USA
> Telephone: +1 212 334 2025
> Fax: +1 212 334 5528
> 
> 
> 
> 
> 
> This message has been scanned by MailController -
www.MailController.altohiway.com
> 
> 
> [Non-text portions of this message have been removed]
> 
> 
>
========================================================================
> Groups related to EnergyPlus_Support 
>
========================================================================
> 
> VisualDOE (27 common members) 
>
http://groups.yahoo.com/group/VisualDOE?v=1&t=ipt&ch=email&pub=groups&sl
k=aftr0&sec=recg
<http://groups.yahoo.com/group/VisualDOE?v=1&t=ipt&ch=email&pub=groups&s
lk=aftr0&sec=recg>  
> Software/Specific Programmes: VisualDOE Software User Group
> 
> paperport (13 common members) 
>
http://groups.yahoo.com/group/paperport?v=1&t=ipt&ch=email&pub=groups&sl
k=aftr1&sec=recg
<http://groups.yahoo.com/group/paperport?v=1&t=ipt&ch=email&pub=groups&s
lk=aftr1&sec=recg>  
> Software/Specific Programmes: PaperPort User Self-Support Forum This
is the Unof...
> 
> OziUsers-L (11 common members) 
>
http://groups.yahoo.com/group/OziUsers-L?v=1&t=ipt&ch=email&pub=groups&s
lk=aftr2&sec=recg
<http://groups.yahoo.com/group/OziUsers-L?v=1&t=ipt&ch=email&pub=groups&;
slk=aftr2&sec=recg>  
> Software/Specific Programmes: A group for users of the OziExplorer
software, inc...
> 
> vendorgsm (8 common members) 
>
http://groups.yahoo.com/group/vendorgsm?v=1&t=ipt&ch=email&pub=groups&sl
k=aftr3&sec=recg
<http://groups.yahoo.com/group/vendorgsm?v=1&t=ipt&ch=email&pub=groups&s
lk=aftr3&sec=recg>  
> Software/Specific Programmes: SOFTWARE AND SOLUTIONS ALWAYS TESTED!
> 
> TC2000-Stocks (7 common members) 
>
http://groups.yahoo.com/group/TC2000-Stocks?v=1&t=ipt&ch=email&pub=group
s&slk=aftr4&sec=recg
<http://groups.yahoo.com/group/TC2000-Stocks?v=1&t=ipt&ch=email&pub=grou
ps&slk=aftr4&sec=recg>  
> Software/Specific Programmes: User's Group dedicated to the discussion
and excha...
> 
> 
> ------------------------------------
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov <http://www.energyplus.gov> 
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
<http://groups.yahoo.com/group/EnergyPlus_Support/> 
> 
> Attachments are not allowed -- please post any files to the
appropriate folder in the Files area of the Support Web Site.
> 
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under
the Documentation link and press the "search" button.
> Yahoo! Groups Links
> 
> 
> 

 

This message has been scanned by MailController
<http://www.mailcontroller.altohiway.com/> .

Click here
<https://www.mailcontroller.altohiway.com/sr/X8HL7KiEjSv53h2eulNQhVmZKVg
WDAKLucTlNbJNFuzjQI12gSE+SadiRWTozhuScJ6Bm8iMShdIRn+lV0DoY3QpYcOcyRLYVS8
JXzn3kKShWXFY7+Xrzc5z!dma9fyIQWc4dhbjaap73W4rH7aDj5tkIXVKYDBAMpjh5gC5soQ
rE!p!iapdUfig+x73kQZv3TG4tFFfWTnnUN2S4oSIOA1bJDV!Wn6a>  to report this
email as spam.



[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/