RE: [EnergyPlus_Support] Water Mains Temperatures
Hi Alan,
The max difference is for over the entire year. You can use the .stat file to figure this out (although it does not explicitly call it out). Taking for example the file "USA_IL_Chicago-OHare_TMY2.stat", find the line called "Monthly Statistics for Dry Bulb temperatures". Now find the line below that called "Daily Avg" which is what is referred to as the "monthly average outdoor air temperature" in the documentation. Here it is reproduced below:
Daily Avg -4.6 -2.2 1.6 8.4 15.3 21.1 23.5 21.8 18.1 11.7 4.2 -2.6
Finally, find the maximum difference between these, in this case it is 23.5-(-4.6) = 28.1 deltaC This is your "maximum difference in monthly average outdoor air temperatures".
P
________________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of alanjackson7
Sent: Tuesday, April 29, 2008 9:03 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Water Mains Temperatures
Could someone elaborate on these two variables for the correlation
calculation. I believe the avg outdoor air temperature is fairly
straight forward, however I am unclear what the max difference refers
too. Max difference in the month? the year? does the .stat or .ddy
explicitly call out these variables? Thanks.
* average annual outdoor air temperature (dry-bulb)
* maximum difference in monthly average outdoor air temperatures
-
aj
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/