I would try to fix 3) first. Check the zone and system sizing objects. 
If you can not find the problem, try pasting in an example Zone Sizing 
object and System Sizing object into an email and send it to the support 
group.

annaliu_67 wrote:
>
> Dear all,
>
> I am working on a 5-zone (3000 sf) UFAD model, and got a few
> questions regarding the simulation results.
>
> 1) There are a lot "heating set-point not met" hours (~2000) for all
> 5 zones. I wonder which air temperature is this report comparing
> with the set-point temperature?
>
> 2) There is a recurring warning, which says "Hot Water flow control
> failed in VS VAV terminal unit zone3 VAV reheat". (This error
> occurred 156 times. Iteration limit (500) exceeded in calculating
> the hot water flow rate.) I feel that this should contribute to the
> first problem. But this may not be the only reason, since other
> zones without the recurring warning also have under heated hours.
> Any suggestions on how to fix this?
>
> 3) Another warning I got is "The design coil load is zero for
> COIL:Water:SimpleHeating MAIN HEATING COIL". What could be wrong for
> this one?
>
> I would appreciate it if you could provide any suggestions. Thank
> you all for your help!
>
> Regards,
>
> Anna
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/