Equation 2 is the heat balance equation without the impact of HVAC
equipment. So this equation is not impacted by airflow through
inlet/outlet nodes in the zone. The actual air mass flow rates used are
shown in the equation as Mi (interzone mixing caused by mixing and
cross-mixing objects) and Minf (infiltration). Each of these mass flow
rate terms represent the mass flow rate of air "entering" each zone and
are specified by the user. The impact of the zone inlet node mass flow
rate on the heat balance is shown in Equation 5 as Msys. This is the
actual mass flow rate "entering" the zone through the zone inlet node
and is a result of HVAC system operation.
anarui.oliveira wrote:
>
> Hi.
>
> A question about E+ heat balance model:
> - What is the actual air mass (I believe it is hidden in "Cz" in Eq.
> (2)?) E+ considers for each zone? Is it constant? Is it affected by any
> of the airflows that use inlet/outlet nodes or zones nodes?
>
> Regards,
> Ana.
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/