Re: [EnergyPlus_Support] Re: PTHP serving two Zones



You have already this, but PTHP and PTAC are single-zone equipment 
models. You will have to use air loop equipment for your application. 
The 2 you list are acceptable.

careym.cosmaj wrote:
>
> Answering my own questions for the benefit of anyone else who reads
> this .... talking to myself, am I mad yet?
>
> > Is this E+'s way of telling me that it does not know what the division
> > of airflow should be?
>
> The division of airflow is done within the DIRECT AIR objects
>
> > Can I use a PTHP to serve multiple zones?
>
> I dont believe so as there is no way of telling a
> PACKAGEDTERMINAL:HEATPUMP:AIRTOAIR which zone temperature to control
> from, while a UNITARYSYSTEM:HEATPUMP:AIRTOAIR can be told which zone
> to use.
>
> > How should I be defining (without autosizing) how much air goes into
> > each zone?
>
> DIRECT AIR objects
>
> > Is there a more simplistic example than 5ZoneAutoDXVAV.idf to consult?
>
> HeatPump.idf is a great start and UnitarySystem:HeatPump:AirToAir in
> Input Ouput Ref is very insightful, pp 818, 823 and 824.
>
>  

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/