[EnergyPlus_Support] About Ground Temperatures
Hi E+
I have problems understanding Ground Temperatures:
I understand that the Ground Temperatures are used as constant (by 
month) temperatures just beneath slab, is it rigth?
I am simulating a non-conditioned space. The slab is simply 10cm of 
concrete with no insulation. The place where it is located is a 
desert with temperatures from 25 (night) to 40ºC (day) in summer. 
After running the Slab auxiliary program, the results are Groun 
Temperatures from 17 to 21ºC. Simulating the dwelling with this 
temperatures and uninsulated slab results in an almost 
perfectly 'conditioned' space because the slab loses heat quite 
rapid. In the real world it's the opposite, the dwelling has 
temperatures of 30-40ºC.
So what's happening? I cannot use these calculated ground 
temperatures since makes the slab lose heat totally unrealistic, but 
I won't use an adiabatic slab since it's also totally unrealistic 
(the temperatures inside the house go to 40-50ºC).
What would physically mean to use the undisturbed temperature of 0.5m 
depth with a slab construction of 10cm concrete and 0.5m of earth?
Regards, 
Daniel
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
    Individual Email | Traditional
<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)
<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/