By the way, the Slab program is really for conditioned spaces.
What you may wish to do is look at the "other
side coefficients" model. This is described in
the IOref as well as the example file
GroundTempOSCCompactSched.idf Another feature is
to have a core and perimeter set of temperatures
-- that is not shown in the example files but can
be done using a "door" in the floor with one set
of temperatures where the slab floor (perimeter)
sees a different set. Some of this is also
described in the Auxiliary Programs document on Ground Heat Transfer.
Here you would set your slab as a surface that
sees temperatures on the other side that may be
more realistic for you. You would still need to
estimate the temperatures used but you may be
able to "play" with those temperatures more
easily and get your measured(?) temperatures inside more realistically.
Ground heat transfer is a real bugaboo for
simulation -- one can make the results be almost
anything you want (or don't want) by setting
ground temperatures too low or too high.
Linda
At 03:26 PM 5/12/2008, Daniel Solís wrote:
>Hi E+
>
>I have problems understanding Ground Temperatures:
[Non-text portions of this message have been removed]
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/