Lym,
What is the reporting interval that you are using? EnergyPlus averages 
the values (or sum when the report variable is Energy) over the 
reporting interval. So when you have boiler working for a few time steps 
and then be off during the rest of the time, the reported value will be 
a time averaged value. So to check, I would start with reporting the 
values at detailed interval (at system time step)

Thanks
Sankar

llyymmff wrote:
>
> Hi,all
> I have another question about the simulation of the boiler.
> When I simulate the constant flow boiler, the simulation result shows
> that the mass flow rate of the boiler is not constant. In some time,
> the value of the mass flow rate is smaller than the design value.
> I cannot understand it. Should the mass flow rate be the constant? Why
> does the constant flow boiler change the flow rate in some time?
> Could you please help me?
>
> Beat Regards!
>
> lym
>
>  

-- 
Sankar Padhmanabhan
Graduate Research Assistant
PhD Student
Mechanical & Aerospace Engg
Oklahoma State University,
Stillwater, OK-74078
Ph:405-744-4380


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/