Re: [EnergyPlus_Support] Re: Invalid air loop component



There may be other ways to do this, but here is my suggestion:

Use DXSystem:AirLoop for the cooling coil and fan, with a Single 
Duct:VAV:Reheat air distribution unit that uses COIL:Water:SimpleHeating 
as the reheat component object.

See example file = 5ZoneAutoDXVAV.idf which is similar to what you are 
looking for, but that example file uses gas reheat coils instead of hot 
water reheat coils.

JV Dirkes II wrote:
> Dear Don,
>
> Following up on your suggestion, I have uncovered a couple more questions:
> The Unitary System or Furnace system are geared toward single zone
> applications (they require a controlling zone"), so they are less
> applicable to my multi-zone requirement.  
> I want to model a Terminal reheat system (ASHRAE 90.1 Baseline system
> #5) with a DX coil and hot water coil which maintain a constant
> discharge air temperature. The DXsystem: object lacks a heating coil,
> though, and I'm now trying to figure out how to add that into the air
> loop.
> It occurs to me that I could let E+ autosize a (relatively) monster
> reheat coil, but I'd rather get it to emulate the real system.  Any
> guidance for adding that heating coil to the air loop?
>
> Thanks!
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Don Shirey <shirey@...> wrote:
>   
>> In an air loop, this DX cooling coil must be included as part of
>>     
> another 
>   
>> "compound component" that controls how the DX coil operates.
>>
>> For example, the DX cooling coil could be part of   DXSystem:AirLoop  
>> or  UnitarySystem:HeatCool
>>
>> JV Dirkes II wrote:
>>     
>>> Dear E+ Forum,
>>>
>>> I'm getting an error which tells me that my coil is an invalid
>>> component.  I doubt that this is really the cause of the error.  Can
>>> someone give a suggestion regarding the cause?  Thanks!
>>>
>>>    ** Severe  ** Invalid Air Loop Component
>>> Type="COIL:DX:COOLINGBYPASSFACTOREMPIRICAL".
>>>    **   ~~~   ** ..Air Loop Component Name="CLGCOIL_AH1".
>>>    **   ~~~   ** ..Air Primary Loop=AIRLOOP_AH1
>>>    **   ~~~   ** ..Air Primary Loop Branch=BRANCH_AIRLOOP_AH1
>>>    **  Fatal  ** Errors found getting Air Primary Loop


[Non-text portions of this message have been removed]


------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/