[EnergyPlus_Support] Operation Scheme Error
Dear E+ Forum,
I have not been able to fix the error below, and will appreciate some
insight and help. There is only one "Plant Operation Schemes" object
in the .idf (as shown below), so I can't figure out what the error
refers to.
** Severe ** More than one Operation scheme scheduled for same
plant loop
** ~~~ ** occurs in PLANT LOOP = PLTLOOP_HTGWATER
** Fatal ** Program terminates due to above conditions.
PLANT LOOP,
PltLoop_HtgWater, !- Plant Loop Name
Water, !- Fluid Type
PltOpernScheme_Htg, !- Plant Operation Scheme List Name
NodeOut_HtgWtr Supply Outlet, !- Loop Temperature Setpoint Node Name
93.3, !- Maximum Loop Temperature {C}
37.8, !- Minimum Loop Temperature {C}
Autosize, !- Maximum Loop Volumetric Flow Rate {m3/s}
0, !- Minimum Loop Volumetric Flow Rate {m3/s}
autocalculate, !- volume of the plant loop {m3}
NodeIn_HtgWtr SupplyInlet, !- Plant Side Inlet Node Name
NodeOut_HtgWtr Supply Outlet, !- Plant Side Outlet Node Name
BrLIST_HtgWtr Supply, !- Plant Side Branch List Name
ConnLIST_HtgWtr Supply, !- Plant Side Connector List Name
NodeIn_HtgWtr Demand Inlet,
NodeOut_HtgWtr Demand Outlet, !- Demand Side Outlet Nodes Name
BrLIST_HtgWtr Demand, !- Demand Side Branch List Name
ConnLIST_HtgWtr Demand, !- Demand Side Connector List Name
SEQUENTIAL, !- Load Distribution Scheme
, !- System Availability Manager List
SingleSetPoint, !- Plant Loop Demand Calculation Scheme
NONE; !- Common Pipe Simulation
PLANT OPERATION SCHEMES,
PltOpernScheme_Htg,
HEATING LOAD RANGE BASED OPERATION,
HtgLdRngBasedOpern_1,
SchCpct_AlwaysOn,
HEATING LOAD RANGE BASED OPERATION,
HtgLdRngBasedOpern_2,
SchCpct_AlwaysOn;
HEATING LOAD RANGE BASED OPERATION,
HtgLdRngBasedOpern_1,
0,
205012,
PltEquipList_Htg;
HEATING LOAD RANGE BASED OPERATION,
HtgLdRngBasedOpern_2,
205012,
410025,
PltEquipList_Htg;
PLANT EQUIPMENT LIST,
PltEquipList_Htg,
BOILER:SIMPLE,
Boiler_Simple1,
BOILER:SIMPLE,
Boiler_Simple2;
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/