Re: [EnergyPlus_Support] Warning: "Air volume flow rate per watt ... is out of range .."
The warning can be an indication of very low supply air flow rate
compared to the coil's cooling capacity.... and very low outdoor air
temperatures may also be contributing.
Find the autosized air flow rate and cooling coil capacity in the .eio
file ... and then look at the COIL:DX:COOLINGBypassFactorEmpirical
documentation in the IO Reference and Engineering Reference for how that
coil model works and how the flow rate/capacity values are used.
JV Dirkes II wrote:
> Dear E+ Forum,
>
> The Air handler for a current E+ model (v2.2) has a
> COIL:DX:COOLINGBypassFactorEmpirical cooling coil and a hot water
> heating coil. The model runs, but has hundreds of instances of this
> warning or "Full load outlet temperature indicates a possibility of
> frost/freeze...", which appears to have a similar cause. All
> capacities are autosized and I am simulating only 3 Design Days with 4
> timesteps per hour (so the hundreds of warnings seem to be too many!)
>
> Will someone help me understand the cause of the error and how to
> resolve it? Thank you!
>
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/