[EnergyPlus_Support] E+ Technique for LEED / ASHRAE 90.1 compliance
Dear E+ Forum,
I'm honing my procedures for using E+ to determine whether a building
meets the LEED certification energy minimum requirements. Since E+
does not allow separate automatic sizing criteria for heating and
cooling systems, it seems that this must be a manual procedure. I
know that many of you have already adopted a procedure and I'm hoping
for some feedback. Here's what I am doing for the Baseline HVAC systems:
1) If the HVAC system is clearly cooling-dominated, I just set the
Sizing Parameters object to 1.15 and nothing else. (similar for
heating-dominated, except using 1.25)
2) If there is a mix of cooling-dominated and heating-dominated zones,
or energy compliance is marginal:
Let E+ autosize all components at 1.0 sizing factor
Once the model is running properly, manually increase sizes as follows:
- Set Zone airflow in Zone Sizing object at max(Clg Airfow * 1.15,
Htg airflow * 1.25)
- Set Baseboard water flow at (autosize * 1.25)
- Set heating pump flows at (autosize * 1.25) with Delta P as
needed for 19W/gpm
- Set cooling pump flows at (autosize * 1.15) with Delta P as
needed for 22W/gpm
- Set Boiler / Heating source capacity at (autosize * 1.25)
- Set Chiller / Cooling source capacity and Heat Rejection
components at (autosize * 1.15)
The above procedure must be repeated for each new building
orientation, which makes it pretty cumbersome....
Does that account for everything?
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/