[EnergyPlus_Support] Unitary MultiSpeed Heat Pump
Hello.
I'm trying to get a Unitary MultiSpeed Heat Pump to work (serving a
single zone, all other zones have PA, which were already working
before introducing the MSHP), but I keep getting node connection
errors and I can't track down where they come from. Could anyone help
figure out where to look?
The errors are as follows:
** Severe ** SET POINT MANAGER:SINGLE ZONE REHEAT: Controlled
Zone not on air loop, Zone=47833
** ~~~ ** Occurs in Set Point Manager=ROOFTOP AHU SUPPLY AIR
TEMP MANAGER
** Fatal ** Errors found in SetPointManager input
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=SET POINT MANAGER:SINGLE ZONE REHEAT:
Controlled Zone not on air loop, Zone=47833
************* Fatal error -- final processing. More error
messages may appear.
************* Testing Individual Branch Integrity
** Warning ** There are orphaned Branches in input
************* All Branches passed integrity testing
************* Testing Individual Supply Air Path Integrity
************* All Supply Air Paths passed integrity testing
************* Testing Individual Return Air Path Integrity
************* All Return Air Paths passed integrity testing
** Severe ** Node Connection Error, Node="ROOFTOP AHU SUPPLY FAN
OUTLET", Sensor node did not find a matching node of appropriate type
(other than Actuator or Sensor).
** ~~~ ** Reference Object=SET POINT MANAGER:MIXED AIR,
Name=ROOFTOP AHU COOLING COIL AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="ROOFTOP AHU HEAT
RECOVERY SUPPLY OUTLET", Setpoint node did not find a matching node
of appropriate type (other than Setpoint, OutsideAir).
** ~~~ ** Reference Object=SET POINT MANAGER:SCHEDULED,
Name=ROOFTOP AHU HEAT RECOVERY AIR TEMP MANAGER
** Severe ** Node Connection Error, Node="46936 SUPPLY INLET",
ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
CONFIGURATION, Name=46936
** Severe ** Node Connection Error, Node="47847 SUPPLY INLET",
ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
CONFIGURATION, Name=47847
** Severe ** Node Connection Error, Node="47799 SUPPLY INLET",
ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
CONFIGURATION, Name=47799
** Severe ** Node Connection Error, Node="47808 SUPPLY INLET",
ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
CONFIGURATION, Name=47808
** Severe ** Node Connection Error, Node="47220 SUPPLY INLET",
ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
CONFIGURATION, Name=47220
** Severe ** Node Connection Error, Node="47252 SUPPLY INLET",
ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
CONFIGURATION, Name=47252
** Severe ** Node Connection Error, Node="47284 SUPPLY INLET",
ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
CONFIGURATION, Name=47284
** Severe ** Node Connection Error, Node="47880 SUPPLY INLET",
ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
CONFIGURATION, Name=47880
** Severe ** Node Connection Error, Node="47833 ZONE EQUIP
INLET", ZoneInlet node did not find an outlet node.
** ~~~ ** Reference Object=CONTROLLED ZONE EQUIP
CONFIGURATION, Name=47833
** Severe ** Node Connection Error, Node="ROOFTOP AHU AIR LOOP
INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outside air inlet node, it must be
listed in an OUTSIDE AIR NODE or OUTSIDE AIR INLET NODE LIST object.
** ~~~ ** Reference Object=BRANCH, Name=ROOFTOP AHU MAIN BRANCH
** Severe ** Node Connection Error, Node="ROOFTOP AHU SUPPLY PATH
INLET", Inlet node did not find an appropriate matching "outlet" node.
** ~~~ ** If this is an outside air inlet node, it must be
listed in an OUTSIDE AIR NODE or OUTSIDE AIR INLET NODE LIST object.
** ~~~ ** Reference Object=ZONE SUPPLY AIR PATH, Name=ROOFTOP
AHU SUPPLY PATH
Regards,
Ana Rui.
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/