[EnergyPlus_Support] Sizing Parameters object has no influence
Dear E+ Forum,
Results of a test are shown below, in which it seems that the Sizing
Parameters object has no influence at all. The Zone Sizing object,
however, works as expected. What might cause the Sizing Parameters
object to not function?
Test 1 Test 2 Test 3
Load (W) Load (W) Load (W)
Zone #1 Cooling 13,288 13,288 15,281
Zone #1 Heating 29,510 29,510 33,937
Zone #2 Cooling 848 848 975
Zone #2 Heating 5,549 5,549 6,382
Zone #3 Cooling 140,762 140,762 161,876
Zone #3 Heating 413,764 413,764 475,829
Remarks Test 1: No Sizing Parameters object, Zone Sizing set at 1.0
Test 2: Sizing Parameters object set for 1.15, Zone Sizing set at
1.0 (No change!)
Test 3: Sizing Parameters object set for 1.0, Zone Sizing set at
1.15 (Expected change)
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/