Dear Richard,

I'm missing something....

Load is 910kW.
Boiler 1 nominal capacity is 205kW
Boiler 2 nominal capacity is 205kW
ONLY Boiler 1 runs (and meets the load, too!  which means it satisfies
a load that is over 400% of its capacity)

p.s., Thanks for your patient and regular assistance.

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad
<RRaustad@...> wrote:
>
> The nominal capacity sets the upper limit (PLR=1).
> 
> Example: Load Range 1 is set at 190 kW and controls only Boiler 1 and 
> Load Range 2 is set at 9999999999W and controls both boilers.
> For loads below 190 kW only boiler 1 can operate. This allows you to 
> pick with equipment will operate in that load range.
> For loads up to 205 kW both boilers can operate but only boiler 1 is
needed.
> For loads above 205 kW, both boilers will operate with boiler 2 
> operating at part-load up to it's full capacity at a total load of
410 kW.
> 
> JV Dirkes II wrote:
> >
> > Fair enough. So what does the "nominal capacity" in the Boiler
object do?
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > <RRaustad@> wrote:
> > >
> > > If the load is 910 kW, then the Load Range needs to account for
that.
> > > The load range does not set the equipment size, it determines which
> > > equipment operates. I'm surprised you didn't see an error in the err
> > file.
> > >
> > > JV Dirkes II wrote:
> > > >
> > > > Dear E+ Forum,
> > > >
> > > > I've just run a model for which I specified the Boiler:Simple
"Nominal
> > > > capacity" for two boilers as 205kW each, The HEATING LOAD
RANGE BASED
> > > > OPERATION is set up so that the upper limit of Load Range 1
was 190kW,
> > > > and the upper limit of Load Range 2 was 380kW.
> > > > For this run, E+ calculates the heating load as 910kW. This
strikes
> > > > me as odd; it seems that the boiler capacity should be limited
to no
> > > > more than 410kW or perhaps 380kW.
> > > >
> > > > Another aspect of this problem is that Pump #2 never operates.
I have
> > > > two branches, each of which has a pump and boiler. The Pump#2 +
> > > > boiler#2 branch never operates, even though it's schedule is
always
> > > > "on". (.svg file shows everything connected as I expect.)
> > > >
> > > > Any suggestions regarding what might cause these problems?
Thanks in
> > > > advance.
> > > >
> > > >
> > >
> > > --
> > > Richard A. Raustad
> > > Senior Research Engineer
> > > Florida Solar Energy Center
> > > University of Central Florida
> > > 1679 Clearlake Road
> > > Cocoa, FL 32922-5703
> > > Phone: (321) 638-1454
> > > Fax: (321) 638-1439 or 1010
> > > Visit our web site at: http://www.fsec.ucf.edu
<http://www.fsec.ucf.edu>
> > >
> > > UCF - From Promise to Prominence: Celebrating 40 Years
> > >
> >
> >  
> 
> -- 
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL  32922-5703
> Phone:   (321) 638-1454
> Fax:     (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
> 
> UCF - From Promise to Prominence: Celebrating 40 Years
>



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/