Apply the availability schedule to the HVAC System (i.e., Furnace or
DXSystem), the coils and the fan objects. If compact HVAC objects are
used, apply the availability schedule to the compact HVAC object. You
will get different results depending on the selection for the night
cycle option.
André Lopes wrote:
>
> Hi Energy Plus Team
> I have the following doubt:
> For example, to make sure that an HVAC System only works from 8h to
> 20h, is it only necessary to create an availabity schedule from 8h to 20h?
> On what HVAC Objects should this schedule be used?
> Regards
> A L
>
>
--