Re: [EnergyPlus_Support] HVAC System availability schedule
Apply the availability schedule to the HVAC System (i.e., Furnace or
DXSystem), the coils and the fan objects. If compact HVAC objects are
used, apply the availability schedule to the compact HVAC object. You
will get different results depending on the selection for the night
cycle option.
André Lopes wrote:
>
> Hi Energy Plus Team
> I have the following doubt:
> For example, to make sure that an HVAC System only works from 8h to
> 20h, is it only necessary to create an availabity schedule from 8h to 20h?
> On what HVAC Objects should this schedule be used?
> Regards
> A L
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/