Re: [EnergyPlus_Support] will the higher cooling coil setpoint affect indoor air temperature control?
You need to maintain enough capacity to meet the load. If the supply air
temperature is increased (delta T from supply air to room air is lower),
the air flow rate should also be increased.
Capacity Q = mCpDeltaT
lichunying83 wrote:
>
> Hello, all
>
> I am doing a simulation, where I supply air with higher temperature
> (17degree centigrade, this is simular with the cooling coil
> setpoint, right?) into a room. The indoor temperature is set to be
> 25degree centigrade.
>
> Now I found that this higher supply air temperature may be affecting
> the control of indoor air temperature. The indoor air temperature
> cannot be maintained at the preset point.
>
> If I reset the cooling coil setpoint to be 16degree centigrade or
> lower, the indoor air temperature control will be OK.
>
> SO I guess the higher cooling coil setpoint may somehow affect
> indoor air temperature control? Is this correct?
>
> Has anyone have encountered this problem before? How to solve this?
>
> Thank you!
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/