Re: [EnergyPlus_Support] help needed regarding example files



Dr. Li:

You mentioned in a previous email that E+ was running on your computer:

------------------------------
There was no problem when both DesignDay and WeatherFile were selected.
------------------------------

If this is the case, the computer/OS/E+ version should not be an issue.

Then you mentioned that it wouldn't run for just weatherfile simulation, and that an 1887 byte error file was produced.  What was in that 1887 byte error file.  That could tell what the problems are.  Please reply with the contents of that file.

Edwin Lee

On Mon, Jul 7, 2008 at 3:30 PM, Yuen Li <yli006@xxxxxxxxxxx> wrote:

Hi, Chirodeep Bakli

EnergyPlus ver.2.2 should run on WindowsXP.
 
If you will explain a liitle more on how you set up the run procedure on your PC, such as ShortCut, start up directory, program link, etc.  I may be able to help.
 
My e-mail ID is:  yli006@xxxxxxxxxxx.  You may contact me directly, if you wish.
 
Dr. Li, Yuan-Lu
Date: Mon, 7 Jul 2008 20:19:13 +0530

Subject: RE: [EnergyPlus_Support] help needed regarding example files

I forgot to mention my EnergyPlus version is 2.2.0.023

--- On Mon, 7/7/08, Yuen Li <yli006@xxxxxxxxxxx> wrote:
From: Yuen Li <yli006@xxxxxxxxxxx>
Subject: RE: [EnergyPlus_Support] help needed regarding example files
To: energyplus_support@xxxxxxxxxxxxxxx
Date: Monday, 7 July, 2008, 1:01 PM

Hi, Chirodeep Bakli
 
What computer are you using?  Have you installed the correct version of Energy Plus software to match the computer or  OS?
 
Dr. Li






To: EnergyPlus_Support@ yahoogroups. com
From: chirodeep@yahoo. co.in
Date: Mon, 7 Jul 2008 12:47:49 +0530
Subject: Re: [EnergyPlus_ Support] help needed regarding example files


No,I am unable to simulate any the example files.
 

--- On Thu, 3/7/08, Richard Raustad <RRaustad@FSEC. UCF.EDU> wrote:

From: Richard Raustad <RRaustad@FSEC. UCF.EDU>
Subject: Re: [EnergyPlus_ Support] help needed regarding example files
To: EnergyPlus_Support@ yahoogroups.. com
Date: Thursday, 3 July, 2008, 11:56 AM

Do any example files run on your PC?

Chirodeep Bakli wrote:
>
> Even after making the changes you suggested the simulation crashes.
>
> --- On *Wed, 2/7/08, Richard Raustad /<RRaustad@FSEC. UCF.EDU>/* wrote:
>
> From: Richard Raustad <RRaustad@FSEC. UCF.EDU>
> Subject: Re: [EnergyPlus_ Support] help needed regarding example files
> To: EnergyPlus_Support@ yahoogroups. com
> Date: Wednesday, 2 July, 2008, 12:17 PM
>
> Notice the Run Control object in example 1A. It says to not do the
> weather file simulation. This file also does not have a RunPeriod
> object
> to tell the simulation which days to simulate from the weather file.
>
> RUN CONTROL,
> No, !- Do the zone sizing calculation
> No, !- Do the system sizing calculation
> No, !- Do the plant sizing calculation
> Yes, !- Do the design day simulations
> No; !- Do the weather file simulation
>
> You will need to add a RunPeriod object. Example below.
>
> RunPeriod,
> 1, !- Begin Month
> 1, !- Begin Day Of Month
> 1, !- End Month
> 12, !- End Day Of Month
> UseWeatherFile, !- Day Of Week For Start Day
> Yes, !- Use WeatherFile Holidays/Special Days
> Yes, !- Use WeatherFile DaylightSavingPerio d
> , !- Apply Weekend Holiday Rule
> , !- Use WeatherFile Rain Indicators
> ; !- Use WeatherFile Snow Indicators
>
> Chirodeep Bakli wrote:
> >
> > Hi
> > I am new to E+.when I try to run the example file 1A with weather
> > input file as the no weather file the simulation crashes.
> > I don't understand what's the problem..can anyone please help me?
> >
> >
> > ------------ --------- --------- --------- --------- --------- -
> > Explore your hobbies and interests. Click here to begin.
> > <http://in..rd. yahoo..com/ tagline_groups_ 6/*http:/ /in.promos.
> yahoo.com/ groups/
> <http://in.rd. yahoo.com/ tagline_groups_ 6/*http:/ /in.promos. yahoo.com/ groups/>>
>
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec. ucf.edu
> <http://www.fsec. ucf.edu/>
>
> UCF -