I brought your IDF into SketchUp through the Energy
Design Plugin. Several things you should fix. First the floor is
upside down. Also two of the walls face the wrong way (in rather than
out): wall4 and wall2. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Deepak Gv Sent: Wednesday, July 09, 2008 3:45 PM To: EnergyPlus_Support@xxxxxxxxxxxxxxx Subject: Re: [EnergyPlus_Support] Heat gain through blinds.
Thank
you very much for your response Dr Hitchcock, As you suggested I tried placing the blinds outside the window. I have observed an decrease in HVAC energy consumption by ~10-15 % on June 21 and ~30% on March 21 when compared to the interior blinds. But as we change the slat angle by closing the external blinds from 0 to 45 angle shows that the HVAC energy drops by only 1.2-3.8%. Closing the exterior blinds from 45 to 90 degree angle shows that the HVAC energy drops by only 1%. Thus there seems to be no effect of closing the blinds on the HVAC Energy consumption due to the heat gained or lost. I would like to know if there is any possible explanation to this. .? I would like to know if my inputs are correct for the outputs that I wish to have. I am attaching the Idf file in the files section. The name of the file would be 2008-07-09 Conventional- -----
Original Message ---- From: Rob Hitchcock <RJHitchcock@ To: EnergyPlus_Support@ Sent: Tuesday, July 8, 2008 6:46:31 PM Subject: Re: [EnergyPlus_ Interior venetian blinds can help control daylight illuminance and visual
glare levels in a space. But, they will not necessarily reduce heat gains
since the solar and thermal gains have already penetrated the glazing before
encountering the blinds. The blinds will warm up and transfer that heat to
the space. EnergyPlus accounts for all of these interactions.
The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.