__._,_.___Dear Josh,
For your consideration:
1) I'm not familiar with any variations of LEED that Canada may be using
2) LEED EA credits require compliance with ASHRAE 90.1, which in turn
requires modeling ALL spaces as heated and cooled (subject to some
anmormal exceptions noted in the Scope statement, par 2.2 and 2.3)
Also note Table G3.1, no. 4 regarding schedules.
3) I think that you can model the mechanical room "cooling" system
with a very high setpoint so that it never operates. Just use the
same setpoints in "Baseline" and "Proposed" systems.
4) You raise a good point regarding possible double counting of fan
and pump motor heat. Although they're small in the overall scheme, I
don't know where E+ puts that heat. For fans, at least, the motor is
often in the airstream and thus part of the cooling load. Not so with
pumps!
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "josh_miarch" <jeemang@...>
wrote:
>
> Howdy All;
>
> I'm preparing a model for a LEED Canada EAc1 submission third party
> review, and I'm curious as to how I should account for the building's
> two mechanical rooms (this is the first LEED submission I've done). In
> this building, they are both within the building envelope, and neither
> is directly conditioned.
>
> The literature says that if they're inside the main building envelope,
> they should be modeled, but doesn't provide much guidance beyond that.
> My thought, based on this, was that I should keep them uncontrolled
> and add some internal gains objects to account for the heat given off
> by the AHUs, pumps, boilers, etc, but I haven't the first clue about
> how I could accurately estimate the heat emitted by this equipment,
> particularly when it would be changing in response to the loads in
> other parts of the building and the ambient temperature in the room.
>
> Alternatively, it was suggested to me that I add a single-zone system
> of some sort (UNIT HEATER perhaps; the building isn't cooled) to
> control it to a relaxed setpoint (16-18 C), which makes some amount of
> sense to me, as it would avoid the problem of having to create a very
> elaborate internal gains schedule. However, the problem I see (and
> perhaps I'm misunderstanding something) is that this would
> effectively double count the inefficiencies of the equipment in the
> mechanical room.
>
> Any suggestions on either method (or another) would be greatly
> appreciated.
>
> Many thanks,
>
> Josh
>
--
Josh Kjenner, EIT, LEED AP
Manasc Isaac Architects Ltd.
10225 100 Avenue :: Edmonton, AB T5J 0A1
780.429.3977
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
![]()
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe
__,_._,___
- Follow-Ups:
- [EnergyPlus_Support] Re: Mechanical Rooms
- From: JV Dirkes II
- References:
- [EnergyPlus_Support] Mechanical Rooms
- From: josh_miarch
- [EnergyPlus_Support] Re: Mechanical Rooms
- From: JV Dirkes II
- Prev by Date: Re: [EnergyPlus_Support] Window operation by wind direction
- Next by Date: Re: [EnergyPlus_Support] Re: Reformulated Electric EIR chiller
- Previous by thread: [EnergyPlus_Support] Re: Mechanical Rooms
- Next by thread: [EnergyPlus_Support] Re: Mechanical Rooms
- Index(es):