[EnergyPlus_Support] Re: need help w/ monthly gas usage results
Dear Dimos,
I took a look at your file and I think your problem is this:
1) You have an ELECTRIC heating coil in the furnace.
2) Since the Furnace is the only heating object, and its coil uses
electricity, there is no load for the Boiler:Steam.
3) Therefore, there is no gas consumption.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "ellinas.1984"
<ellinas.1984@...> wrote:
>
> Hello group,
> The facility I am modeling has two boilers. I specified one of them
> under the boiler object in EnergyPlus just to see how it would run. I
> also specified the gas rate schedule. However, when I run the
> simulation and view the results, I get values of zero for the monthly
> gas usages. Unlike the results from the electricity rate schedule that
> I specified, where it shows the monthly usage in the results, I get
> nothing for the gas. Is there anyone out there that knows how to help
> me solve this problem?
>
> Thank you,
> Dimos
>
> p.s. I uploaded my idf file. It is bakery3.idf with the subtitle "gas
> rate usage values" under the problem submittal folder.
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/