Thanks for the help. I now understand why I'm not getting values. However, my ultimate goal is to obtain monthly gas usage values for one boiler and 4 ovens for the facility I am modeling. Since I'm trying to model a boiler and 4 ovens, could I just simply specify the total power input from the boiler and ovens (in watts) under the GAS EQUIPMENT object? When I did that, I got an error in my simulation. Or do I need to use the boiler object and something else for the ovens? I'm still struggling with trying to get gas usage values for this part of my work. Any help or suggestions would be appreciated.
 
Thank you,
Dimos

--- On Mon, 7/28/08, JV Dirkes II <jvd2pe@xxxxxxx> wrote:
From: JV Dirkes II <jvd2pe@xxxxxxx>
Subject: [EnergyPlus_Support] Re: need help w/ monthly gas usage results
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Date: Monday, July 28, 2008, 12:48 PM

Dear Dimos,

I took a look at your file and I think your problem is this:

1) You have an ELECTRIC heating coil in the furnace.
2) Since the Furnace is the only heating object, and its coil uses
electricity, there is no load for the Boiler:Steam.
3) Therefore, there is no gas consumption.

--- In EnergyPlus_Support@ yahoogroups. com, "ellinas.1984"
<ellinas.1984@ ...> wrote:
>
> Hello group,
> The facility I am modeling has two boilers. I specified one of them
> under the boiler object in EnergyPlus just to see how it would run. I
> also specified the gas rate schedule. However, when I run the
> simulation and view the results, I get values of zero for the monthly
> gas usages. Unlike the results from the electricity rate schedule that
> I specified, where it shows the monthly usage in the results, I get
> nothing for the gas. Is there anyone out there that knows how to help
> me solve this problem?
>
> Thank you,
> Dimos
>
> p.s. I uploaded my idf file. It is bakery3.idf with the subtitle "gas
> rate usage values" under the problem submittal folder.
>


__._,_.___

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___