Edwin,
Thank you very much for your support
Actually, I created those two RunPeriod:Design objects and specified Design Day within both the Zone Sizing and Sytem Sizing.
I run a simulation but I have got a severe error:
** Severe ** Zone Sizing calculations need Design Day input
** Fatal ** Errors found in getting ZONE SIZING input
as I used 'RunPeriod:Design' instead of 'DesignDay'
Kind regards,
Sherif
----- Original Message ----
From: Edwin Lee <leeed2001@xxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Monday, August 4, 2008 1:34:53 PM
Subject: Re: [EnergyPlus_Support] Summer/Winter Design Days for system autosize
Sherif:
I took a quick look at the zone sizing calculations, and at first glance, it appears that these design run periods are treated the same as design days. The zone sizing module contains loops that loop across all 'regular design days' and all 'run period design days'. If using the 'design day' key doesn't seem to size the zone/equipment properly, or if it gives any errors, I will investigate further.
Thanks,
Edwin
On Mon, Aug 4, 2008 at 6:11 AM, Sherif Ezzeldin <shezzeldin@yahoo. com> wrote: