Dear All,
At present I have finished the model exercise for the
"BenchmarkLargeHotel" and I´m debugging the errors from the simulation.
I have encountered the following error:
** Warning ** PlantCondLoopSupplySideManager: No Setpoint Manager
Defined for Node=TOWERWATERSYS SUPPLY OUTLET NODE in plant condenser
loop=CONDENSER LOOP
** ~~~ ** Add Temperature Setpoint Manager with Control
Variable = "TEMP" for this Condenser Loop.
** Fatal ** Previous severe set point errors cause program
termination
After comparing the two idf files (mine and the one from the example
files data sets), I cannot figure out why this error is appearing
since both have the setpoints defined in the same way and in the same
number. The solution file does not complain about a need for a another
setpoint manager. Can you have a look at my idf file and give me some
guidance help?
Thanks in advance,
Nuno
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/