Look at the example file HeatPumpWaterHeater.idf. In your file, hook up
the plant loop to the USE SIDE nodes in the WaterHeater:Mixed object.
Just use a 1 for the use side effectiveness value.
HEAT PUMP:WATER HEATER,
Zone5HeatPumpWaterHeater,!- Heat Pump Name
HeatPumpWaterHeaterSch, !- Availability Schedule Name
HPWHTempSch, !- Heat Pump Compressor Set Point
Temperature Schedule Name
2.0, !- Dead Band Temperature Difference {deltaC}
HPWHWaterInletNode, !- Condenser Water Inlet Node Name
HPWHWaterOutletNode, !- Condenser Water Outlet Node Name
autocalculate, !- Condenser Water Volumetric Flow Rate {m3/s}
autocalculate, !- Evaporator Air Volumetric Flow Rate {m3/s}
Zone and Outdoor Air, !- Inlet Air Configuration
HPWHAirOutletNode, !- Heat Pump Air Inlet Node Name
HPWHAirInletNode, !- Heat Pump Air Outlet Node Name
HPWHOutdoorAirInletNode, !- Outside Air Node Name
HPWHExhaustAirOutletNode,!- Exhaust Air Node Name
, !- Inlet Air Temperature Schedule Name
, !- Inlet Air Humidity Schedule Name
SPACE5-1, !- Inlet Air Zone Name
Water Heater:Mixed, !- Water Heater Tank Type
HPWHTank, !- Water Heater Tank Name
, !- Water Heater Tank Use Side Inlet Node Name
, !- Water Heater Tank Use Side Outlet Node Name
Coil:DX:HeatPumpWaterHeater, !- DX Coil Type
HPWHDXCoil, !- DX Coil Name
5.0, !- Minimum Inlet Air Temperature for Heat
Pump Compressor Operation {C}
Zone, !- Compressor Location
, !- Compressor Ambient Temperature Schedule Name
Fan:Simple:OnOff, !- Fan Type
HPWHFan, !- Fan Name
Draw Through, !- Fan Placement
15.0, !- On-Cycle Parasitic Electric Load {W}
5.0, !- Off-Cycle Parasitic Electric Load {W}
Zone, !- Parasitic Heat Rejection Location
HPWHInletAirMixerNode, !- Inlet Air Mixer Node Name
HPWHOutletAirSplitterNode, !- Outlet Air Splitter Node Name
HPWHMixerInletAirSch; !- Inlet Air Mixer Schedule Name
WATER HEATER:MIXED,
HPWHTank, !- Name
0.3785, !- Tank Volume {m3}
Hot Water Setpoint Temp Schedule, !- Setpoint Temperature Schedule
2.0, !- Deadband Temperature Difference {deltaC}
82.2222, !- Maximum Temperature Limit {C}
CYCLE, !- Heater Control Type
5000, !- Heater Maximum Capacity {W}
0, !- Heater Minimum Capacity {W}
, !- Heater Ignition Minimum Flow Rate {m3/s}
, !- Heater Ignition Delay {s}
ELECTRICITY, !- Heater Fuel Type
0.95, !- Heater Thermal Efficiency
, !- Part Load Factor Curve
10, !- Off-Cycle Parasitic Fuel Consumption
Rate {W}
ELECTRICITY, !- Off-Cycle Parasitic Fuel Type
0, !- Off-Cycle Parasitic Heat Fraction To Tank
30, !- On-Cycle Parasitic Fuel Consumption Rate {W}
ELECTRICITY, !- On-Cycle Parasitic Fuel Type
0, !- On-Cycle Parasitic Heat Fraction To Tank
ZONE, !- Ambient Temperature Indicator
, !- Ambient Temperature Schedule
SPACE5-1, !- Ambient Temperature Zone
, !- Ambient Temperature Outside Air Node
2.0, !- Off-Cycle Loss Coefficient To Ambient
Temperature {W/K}
1.0, !- Off-Cycle Loss Fraction To Zone
2.0, !- On-Cycle Loss Coefficient To Ambient
Temperature {W/K}
1.0, !- On-Cycle Loss Fraction To Zone
0.00379, !- Peak Volumetric Use Flow Rate {m3/s}
Hot Water Demand Schedule, !- Use Flow Rate Fraction Schedule
, !- Cold Water Supply Temperature Schedule
, !- Use Side Inlet Node
, !- Use Side Outlet Node
, !- Use Side Effectiveness
HPWHWaterOutletNode, !- Source Side Inlet Node
HPWHWaterInletNode, !- Source Side Outlet Node
0.95; !- Source Side Effectiveness
COIL:DX:HEATPUMPWATERHEATER,
HPWHDXCoil, !- Coil Name
4000.0, !- Heating Capacity {W}
3.2, !- Rated COP {W/W}
0.6956, !- Rated SHR (gross)
29.44, !- Rated Evaporator Inlet Air Dry-Bulb
Temperature {C}
22.22, !- Rated Evaporator Inlet Air Wet-Bulb
Temperature {C}
55.72, !- Rated Condenser Inlet Water Temperature {C}
autocalculate, !- Rated Evaporator Air Volumetric Flow
Rate {m3/s}
autocalculate, !- Rated Condenser Water Volumetric Flow
Rate {m3/s}
No, !- Evaporator Fan Power Included in Rated COP
No, !- Condenser Pump Power Included in Rated COP
No, !- Condenser Pump Heat Included in Rated
Heating Capacity and Rated COP
150.0, !- Condenser Water Pump Power {W}
0.1, !- Fraction of Condenser Pump Heat to Water
HPWHInletAirMixerNode, !- Evaporator Air Inlet Node Name
HPWHDXCoilAirOutletNode, !- Evaporator Air Outlet Node Name
HPWHWaterInletNode, !- Condenser Water Inlet Node Name
HPWHWaterOutletNode, !- Condenser Water Outlet Node Name
100.0, !- Crankcase Heater Capacity {W}
5.0, !- Maximum Ambient Temperature for
Crankcase Heater Operation {C}
wet-bulb temperature, !- Evaporator Air Temperature Type for
Curve Objects
HPWHHeatingCapFTemp, !- Heating Capacity Modifier Curve Name
(function of temperature)
, !- Heating Capacity Modifier Curve Name
(function of air flow fraction)
, !- Heating Capacity Modifier Curve Name
(function of water flow fraction)
HPWHHeatingCOPFTemp, !- Heating COP Modifier Curve Name
(function of temperature)
, !- Heating COP Modifier Curve Name
(function of air flow fraction)
, !- Heating COP Modifier Curve Name
(function of water flow fraction)
HPWHPLFFPLR; !- Part Load Fraction Correlation Name
(function of part load ratio)
anarui.oliveira wrote:
>
> Maybe this additional information helps:
>
> ...I started out with a model of a boiler created with Compact HVAC,
> and then expanded it and substituted the boiler by the Heat Pump Water
> Heater.
> The expanded model with the boiler works fine... so I guess I missed
> something when adapting it to a model with a heat pump?...
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>, "anarui.oliveira"
> <anarui.oliveira@...> wrote:
>
> Hi everyone.
>
> I modelled a system with a central Heat pump (air-to-water), producing
> heat for a hot water loop serving 3 Air Treatment Units and some
> terminal unit ventilators, but the thermal heating rate/energy produced
> by the central heat pump is much (2-3 times) higher than the sum of the
> heating rates/energy of all the coils in the ATUs and terminal units...
> It seems as if the control os this central unit is not performing
> properly, but I can't figure out why...
>
> Could anyone help?
>
> Thanks in advance,
> Ana Rui.
>
> --- End forwarded message ---
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are not allowed -- please post any files to the appropriate folder in the Files area of the Support Web Site.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/